Thread: 3-way switch
View Single Post
  #2 (permalink)  
Old 04-06-2005, 11:31 PM
kactuskid's Avatar
kactuskid kactuskid is offline
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
Thanks: 0
Thanked 0 Times in 0 Posts
kactuskid is on a distinguished road
I'm guessing you're using a digital voltage meter to take your readings. If you are, then what you're reading is called Phantom voltage. This actually means there is no voltage there. If you measure using an analog meter you will read nothing. No worries, everything is operating as it should. Here's a link that'll explain the details for your.

http://www.essexep.com/electrical/techinfo/voltage.htm
Reply With Quote