Rheem air handler fan

Greetings. I turned on the AC for the first time the following occurred. The outside AC unit operated fine with the the compressor getting cold. In the air handler (Rheem RHQA-1600B) the evaporator coils also became cold, but blower stopped. Inside the air handler panel I found a terminal and capacitor corroded from salt water complimants of flodding from Hurricane Isabel. All other connections in the airhandler are hot. I researched the capacitor to be 10 MFD, 370 volts and replaced the terminal. Any tips on installing the capacitor andsequencing??

Thanks