Thread: Freon question
View Single Post
  #2 (permalink)  
Old 08-19-2006, 11:56 PM
LazyPup's Avatar
LazyPup LazyPup is offline
Deity
 
Join Date: Apr 2004
Location: Youngstown, Ohio USA.
Posts: 2,260
Thanks: 0
Thanked 17 Times in 17 Posts
LazyPup has a spectacular aura about
I appologize for my delay in responding but this is a very short post which raises a number of rather complex and potentially controversial questions which required a bit of thought on how to address it.

While I am sure there are two sides to every story, based solely upon the information presented here my first reaction would be to say this would be the last time that service tech worked on my system.

In the residential and commercial HVAC industry the accepted method of dealing with leaks in a system is to use an Electronic Halogen Leak Detector to locate the leak then take the necessary steps to make a permanent repair.

Some refrigerants cause rapid deterioration of neoprene O-rings used in fittings and there are a number of "Stop Leak" products designed to address that particular problem, however, while neoprene O-rings are common in automotive AC systems in residential systems nearly all joints are brazed copper or flare fittings which do not have neoprene O-rings thus the use of the stop leak products is marginal at best and in many cases it will void the warranty on your compressor and can cause problems with compressors and expansion valves.

While there is no mention of it in the post,I feel it fair to mention here that there is also a Leak Detector Dye that can be put in the refrigerant. These products should also be strongly avoided.

Now for the Refrigerant charging technique. When a refrigerant cylander is upright there is a pocket of gasseous refrigerant at the top of the cylander. As the refrigerant gas is drawn off the ambient air heat surrounding the cylander boils some of the liquid to a gas to maintain equal pressure in the cylander. The gasseous refrigerant is drawn into the low side or suction line of the AC unit by the compressor.

If the refrigerant cylander is turned upside down the pocket of pressurized refrigerant gas is above the liquid and it pushes liquid refrigerant down into the charging manifold. Under idea conditions that liquid refrigerant will boil to a gas in the charging manifold lines and enter the AC as a gas and this technique is used by some technicians to speed up the charging process but there is a very high risk that some of the liquid refrigerant will carry into the AC unit and get sucked into the compressor cylander. Liquid is not compressible so when this occurs we hear a very loud knocking noise which is known in the trade as "Slugging". This is a very risky procedure because slugging can cause permanent damage to the compressor valves and this method should be avoided.

Having said that, there is a device manufactured by Imperial Eastman Corp called a "Kwik Charge" that can be attached to a refrigerant cylander, then the charging manifold is attached to the kwik charge. With this device we can keep the refrigerant cylander upside down thereby forcing the liquid into the Kwik charge where it is converted to a gas before entering the charging manifold. (See the attached illustration.)

Under no circumstances should a technician ask a customer or untrained individual to hold a refrigerant tank while charging, especially if the tank is upside down. While it is extremely rare, none the less, the risk is present that the charging manifold could come loose and permit some of the liquid refrigerant to spray out. At standard atmospheric pressure the boiling temperature of R-22 is approximately -41 degF. Ask any experienced HVAC tech and they will confirm that even a drop of liquid on your skin will result in instant frostbite and if it should happen to splash in your eye it could freeze the eyeball and cause blindness. Refrigerant tanks should not be handled by anyone who has not been properly trained, especially when the valve on the tank is open.

The pressure you found printed on the data plate are factory test pressures and do not reflect the correct operating pressure. The good news is the pressures you noted on the guages is the correct pressure for an AC operating on a 93degF day.

Now for your question about the pressure range on the charging manifold guages.

A PSIA guage would indictate PSI-absolute which indicates all pressure above absolute zero thus a PSIA guage would show standard atmospheric air pressure at approximately 14psi.

The RED guage on a charging manifold is calibrated as a PSIG guage. On the PSIG scale the meter is calibrated to show zero at standard atmospheric pressure and the pressure indicated is PSI above standard atmosphere. The guage is the calibrated from zero to 350 or 400psi which is the highest operating pressure we are likely to encounter on an AC when the compressor is running.

The BLUE guage commonly called the Low Side guage is calibrated as a "Compound guage." On a compound gage pressures above standard atmospheric pressure are calibrated as PSI readings and printed in black on the guage, while pressure below atmospheric pressure, commonly called vacuum pressure are calibrated in "Inches of Mercury" (in/Hg) and printed in red on the guage. For AC refrigerants the low side pressure will normally be 70psi or less so there is no need for the guage to go higher. For refrigeration the normal low side pressures will typically be under 10psi and many refrigerators operate with a vacuum on the low side.

We also use the vacuum guage when pulling vaccuum on the system to insure it is properly dehydrated prior to charging the refrigerant or to test for leaks.
Attached Images
File Type: jpg refrigerant tank.JPG (55.2 KB, 5 views)

Last edited by LazyPup; 08-20-2006 at 04:08 PM..
Reply With Quote