when you shut off power the blower stops. when you turn it back on does the blower start again? I mean right away? if it does then the blower contactor has welded contacts or the control coil is burnt and has expanded holding the crossarm in the closed position. in this case (either) change out the contactor or at least the control coil if it was the latter.
|