The plumbing code says the floor must have a minimum pitch of 1/4" per foot downwards towards the drain but no portion of the floor may pitch more than 1/2" per foot.
The code also requires that the elevation of the threshold must be a minimum of 2" higher than the finished elevation of the drain therefore you would need a minimum of 4' from the drain opening to the doorway with a 1/2" per foot pitch or a minimum of 8 feet from the doorway to the drain with a 1/4" per foot pitch.
|