I'm getting near the end of my rope, but luckily I found this forum (and intend to explore others as time allows).
I've got an early '90s Bryant Plus 90, Model398AAZ06060AAKA. It worked flawlessly up until two years ago, when it started to intermittantly not start up, but let me explain. In the sequence of events, no one (myself or any furnace repair guy) has ever been able to witness for the sake of troubleshooting what exactly takes place (the nature of intermittant), but here is the outline:
The inducer motor/fan will start up in response to the thermostat, but it quits before the burner ever comes on. Whether or not the pilot light makes it on is anybody's guess. This apparently puts the electronics into a lockout mode. If you switch off the furnace, either with the main power switch (furnace mounted) or at the thermostat, then switch back on, it will come back and start over, this time successfully. The furnace will work normally for anywhere from 24 hours to two weeks, then will fail again, whereupon you can reset it with the power off/on routine and go from there, with the results being another undetermined length of normal service.
The service people who've work on this thing have kind of come to an impass, and I've educated myself on the sequence of operations, based on the manuals that came with the furnace, so I could do my own troubleshooting, as I have a background in electronics. Not that I have anything against service people, but it has simply become a matter of parts swapping, as they don't seem to have any broad history of this particular problem to go by (plus it's expensive!), so I've turned to the 'Net to see who might be able to help.
Let me also say that, along the same time this problem started to develop, a leak in the secondary heat exchanger was detected (water in the blower compartment and then on the floor -- never to any level that would immerse the electronics), and that was replaced recently.
The service techs started out checking the inducer intake for obstructions -- no problem there. Then they swapped out the ignitor/lockout module (ILO -- a logical choice as I've come to learn). But because the furnace never fails in the presence of anyone (could take weeks), they pack up and consider it solved, until we call again. Generally, if someone is home, we just switch off/on the furnace and keep the house warm. The ILO has been changed twice!
Then the following parts have all been replaced: The inducer motor relay board; the pressure switch; the inducer motor itself (which, when it didn't solve the problem, they swapped back out for the old one, fortunately for me); the thermostat itself; the pilot assembly; the blower control PC board. I also, on a hunch, decided recently to bypass (put a jumper on) the high-temp limit switch, thinking that this might have become degraded due to the water possibly being blown around in the blower compartment from the leaky exchanger. Nope. It still fails and must be reset with the off/on routine.
The only thing left I can think of is that there's a problem in the redundant gas valve, perhaps with the opening of the pilot gas flow, but that's why I'm here today, folks. Keep in mind, the inducer motor seems to shut off early in the sequence, before the burners are ever on (that's what I keep trying to assess, but I'm never there or paying close enough attention when it shuts off).
Does anyone have a clue what might be going on with this thing? I'm not inclined to have the gas valve replaced unless the evidence is strong (mucho dinero, you see). I know the problem must be electrical/electronic in nature, but practically every part has been replaced. Has anyone ever had a problem with the 115VAC/24VAC transformer becoming intermittant? Haven't replaced that part yet. Or any electrical connectors becoming corroded, perhaps just a ground connection? Things in both compartments actually look pretty clean.
Aren't there any diagnostic devices devised that can be connected up to this to more closely pinpoint the area of trouble? That would be a good electronics class project!
I need help, or I may have to get a new furnace, which the two local outfits that sell/service Bryant would love to provide! But really, this has got to be something so simple. Everything else works fine on it, and it's only 15 yrs. old or so. Just a baby, really. But the services techs can't apply themselves in this sort of a problem for any length (understandably), so I'm trying to find out the fix myself. HELP!
|