HayZee, thank you. You have been most patient. I have decided really do my homework on this, and in doing so, realized that I have any additional problem. I have e-mailed you an exact diagram of the electrical system.
Two issues:
1) When I turn on thermostat 2, (as you can see by the wiring), it does energize RA89A relay and Circulator 2, but it also energizes thermostat 1, which in turn energizes L8148E and Circular 1, thereby heating both zones of the house. Which is obviously NOT what I want. How should it be wired, so that each system goes on independently of each?
2) I still am confused as to where I connect the yellow and red wires of V8043 to the system. I am mostly confused because I do not get a 24v reading on any terminal other than the thermostat terminals. Based on the diagram, can you tell me exactly which terminal I would connect them to?

Please help. Thank you!!!