Unhappy Sealed refrigeration system problem

Quote:
Originally Posted by govtdog

I had a service guy come out and he thinks the fridge is a goner, since only the bottom half of the cooling coils freeze up and not the top half? He said that is caused by a freon leak somewhere in the coils...
Not necessarily but a refrigeration system problem for sure (see the following link).

LINK > How does a frost free refrigerator's defrost system work?

Quote:
I heard that this fridge uses two separate heaters/defrosters... so I am wondering if could it be just that the top heater/defroster works, and not the bottom one, thereby causing the freezeup?
I'm afraid not. The heaters are wired in series. If one failed, the other would stop working as well. Sorry.

Quote:
and that it would be cheaper to buy a new fridge rather than replace the entire coil assembly.
Did he actually find a problem with the "coil assembly"?

In any case, a refrigeration system problem will usually be expensive to correct. IF just a leak and it can be be isolated and repaired without replacing parts, probably $150+. If it needs parts (evaporator or compressor, etc.) to correct it, it could easily be $350+. While cheaper than a new fridge, it is borderline as to whether the repair would be worthwhile or not.

JMO

Dan O.