Run a length of 6/3 armored cable to each disconnect. Use armored cable for mexhanical protection. You can nail the armored directly to your joist face. Romex is a no no unless you bore holes at approx center of the joist or provide running boards along your staple path. Use the armored from the disconnect to the terminal box of each kiln. Use "greenfield" connectors for the armored cable.