Get an electronic meter, meaure the voltage a the W terminal at the furnace while the stat is in night set back mode and catch it in action. You will see 24 or so volts while it is calling and the burners should light up. The 24 volts should drop off and the burners shut off. If the 24 volts stays up and the burners shut off then the furnace has the problem.