Posts: 3,594
|
|
|
because you have a solid path back to the main neutral bus [ the bare ground and the white cable] one breaker will trip. [on the affected circuit] the enclosure case will be bonded to the common neutral back at the main panel so any fault to the metal ground will cause it to trip. any short to the white will also trip the affected circuit breaker.
|