Quote:
Originally Posted by spotty View Post
I typicaly run a 12-3 and use two seperate receptacles
May I ask why? Both a washer and gas dryer are perfectly fine on a shared 20A circuit.


Quote:
Originally Posted by spotty View Post
At least these two outlets don't have to be GFI or AFCI protected,
They absolutely DO need GFI protection IF they are within 6' of a laundry sink.


Tamper-proof ONLY applies to areas who have adopted the 2008 NEC with no amendments for that section.
NOT nearly every place has.