Quote:
Originally Posted by spotty View Post
how many people have a wet sink within six ft of the outlet,
Ummm, a lot! I have a laundry sink RIGHT next to my washer.

I suggest you read 210.8(A)(7).
In fact I'll post it for you:

210.8 Ground-Fault Circuit-Interrupter Protection for Personnel

(A) Dwelling Units
All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel.

(7) Laundry, utility, and wet bar sinks — where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink



NO ifs ands buts OR exceptions. GFI protection IS required even if the receptacle is behind the washer or dryer.




Quote:
Originally Posted by spotty View Post
and a motor on a gfi circuit can become a nuciance trip.
So what.
__________________
No, that's not me in the avatar. I just like the picture.