The ONLY way this can work is with a "3-wire" (12/3, 14/3) between receptacle 1 & 2, BUT there is NO way to GFI protect both receptacles.
OK, actually one way. You would need "4-wire" (12/4, 14/4) between the receptacles, but this gets tricky, and good luck trying to find a place that will cut 4-wire. GFI's are cheap anyway.
Do it with a 3-wire in between the use a GFI receptacle at each location wired to LINE side.