some jurisdictions allow a homeowner permit for electrical. in massachusetts where I wired houses they had an uninsured installers waiver for insurance. that way if something cooked they couldn't come back on me. [thankfully nothing ever did - 37 houses] check the size of the conductors coming out of the meter socket. all the power co is gonna do is pull the meter put some insulators on the stabs and shove the meter back in place and reseal it. you might consider replacing the wires from the load side of the meter to the new panel because they are never the correct length. make sure you use no-alox anti oxidant on all connections. torque is mentioned on the panel's nomenclature paper so many foot pounds or inch pounds. rule of thumb tighten it then wait a few minutes then retighten, then leave it alone.