No-alox is good on all conductors most especially the service entrance conductors Cu or Al. But you hardly see it at outlet and switch terminations because it's so messy. In the case of aluminum branch conductors I'd use it but you hardly see aluminum on branch circuits. Use it if you have copper clad aluminum but again here's a conductor you hardly ever seen used. inside the meter enclosure are four stabs. two up top are the line, two at the bottom are load. right smack in the center between the four meter landings is the neutral clamps (2) the load is on the bottom along with a driven ground IF you utility uses this as the equipment ground or driven ground location. I may have a meter enclosure in my garage. I'll go look and submit a picture.