05-14-2008, 12:50 PM
|
 |
Deity
|
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,670
|
|
|
Yeah, no problem - you understood correctly. what I was referring to in the latter portion was that if your output from the meter trough to the poanel is SEU cable then you would use non weather tight connectors to secure the cable to both the meter trough and panelbox. If your run to the panelbox was to be in conduit, PVC then you'd use three conductors AND if the conduit run was metal, that you'd need to use bonding bushings at both ends along with a stranded #6 copper ground between the bonding bushings. you see I know its hard to explain but grounding and bonding are two different things in the electrical code.
|