service entrance
look at the diagram. the ground from the driven ground rod is one piece to the neutral in the meter socket. another piece of bare 6 goes from the meter socket bonding bushing through the bushing's lug down in the conduit to the panelbox's bonding bushing's lug and through to the neutral strip. one piece of wire goes from the house waterpipe's clamp, through two clamps around the water meter all the way to the panel box's neutral strip. so at the panel box's neutral you will have one bare ground from the water pipe, one bare from the bonding system and one black/white tape from the meter neutral.
|