Kidd6488 - a bare ground is connected to the auxillary ground bar ONLY if it is in a sub panel -or- if there is one installed in the main panel. Normally in a main panel the neutral bus is bonded to the equipment ground through a heavy duty jumper wire or a bonding screw,
Lazypup - the only place I've seen a manual disconnect and servicing receptacle is in a refrigeration location remote from a panel disconnect. Can you or would you quote me the NEC section and sub section?
|