Well the fan is 50CFM and the bathroom is 245f^3. I only need a 32CFM fan for a bathroom that size, therefore, the fan is more than adequate. Since the shower is in the corner I don't think there is much I can do, the fan would have to be moved to right above the shower stall, that would require ripping out my drywall cieling and wall to run more pipe and a longer conductors...not going to happen.
There is a fairly big gap under the door so all the air is probably coming in from there. I wonder if I could put a little sweep under the door so air is more restricted and take more paths in the bathroom to the fan?
|