Mostly, the pilot will stay on when this happens. Pilot lights, time passes, burners light and then burn out, pilot stays lit, as burners fire back up and then burn out again.
I do have a meter and tried to check control voltage, but wasn't sure which leads were the main selenoid. The gas valve has 5 connections labeled from back to front 5,1,4,2,3. I attached a picture of it I found. I checked voltage on 5 and 1 since that was closest to the selenoid, and I do seem to get a consistent 24-25 volts as burners are going on and off, and no voltage when everything is idle...but is that the right terminals?
I will try to dig into the pilot assembly tonight and clean it with a wire toothbrush or something....but what do you think?