View Single Post
  #2 (permalink)  
Old 03-22-2009, 03:06 PM
Redwood's Avatar
Redwood Redwood is offline
Handyman
 
Join Date: Feb 2009
Location: Connecticut
Posts: 159
Thanks: 10
Thanked 15 Times in 14 Posts
Redwood will become famous soon enough
I do not think your T&P valves have failed.
I think they are working exactly as designed to do.

A T&P valve discharges for 2 reasons Temperature & Pressure.
Most in a residential application will discharge at 150 Psi. or, at 210 Degrees F.

You need to take some tenperature & pressure measurements to determine the cause, Most of the time we see a discharge due to thermal expansion. Usually a discharge of about a coffee cup or 2.

Do you have a pressure reducing valve installed on your house?
Go you have an expansion tank installed on your water heater?
__________________
I stayed at a Holiday Inn Express last night.
Now I can Plumb!
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.


For great information on the history of sanitary sewers including the use of Redwood Pipe
Visit
To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
Did you know some Redwood Pipe is still in service today.
Reply With Quote