I do not think your T&P valves have failed.
I think they are working exactly as designed to do.
A T&P valve discharges for 2 reasons Temperature & Pressure.
Most in a residential application will discharge at 150 Psi. or, at 210 Degrees F.
You need to take some tenperature & pressure measurements to determine the cause, Most of the time we see a discharge due to thermal expansion. Usually a discharge of about a coffee cup or 2.
Do you have a pressure reducing valve installed on your house?
Go you have an expansion tank installed on your water heater?