this all above may be well worth the reading but I have never seen a load [i.e. a motor] fed off the control side of a control transformer. the motor comes off the line side of the circuit. the OP says a 5 amp fuse is blowing. A quarter hp motor draws 1.5 amp when its running. I would look into the control circuit for a burnt up control relay coil or a reversing valve IF it's 24 volt!