Thread: New Sub Panel
View Single Post
  #3 (permalink)  
Old 02-18-2003, 01:02 PM
kliot kliot is offline
New Member
 
Join Date: Feb 2003
Location: Orinda, CA, USA.
Posts: 3
kliot
You will need a 100 amp tie-bar breaker for the main panel. Wire size will depend on wire rating 60C or 90C, copper or alum. how far is the new sub panel from the main, voltage drop is an issue as distance increases. I'm not a electrician but if I recall you will need 4-4 90C thhn copper wire for a 100 amp sub. panel.

Perrin
Reply With Quote