These plans keep evolving, so bear with me. It doesn't help that my electrician who said he would design and hook-up everything now won't return my calls.

My needs at boathouse (sub-panel 40 ft. away from hoist):

13.5 amp, 1HP hoist
1-flourescent work light
1-60w fixture
1-double floodlight fixture
1-110v receptacle

along the trail:
5-double floodlight fixtures (last 300 ft. of run)

From the advice here and elsewhere, I've decided to run 3-#2awg wires (includes 1 neutral) plus a #8 ground, in 2" PVC. There is a 90deg. turn at about 280 ft. into the run, so I'm thinking about an elbow pull (removable plate, 90 deg. elbow) at this point. Then I guess I will pig-tail to each trail light at a box and pull from there?