Minimum size wire for a 90 foot run at 50 amps is a #6 thw/thwn copper.
For a 240 volt circuit minus a neutral you'll need three conductors - two hots and an equipment ground. Because you have no direct burial access, run everything in PVC plastic with appropriate fittings to overcome right angle runs. See illustrations on electrical fittings. (LB, LL, LR etc)
Use 1 inch trade sized PVC conduit.
|