What he has is 3 separate 15 KVA 600V - 120V dry type transformers wired in " Delta-Wye " to give him your typical 120/208V 3 phase 4 wire service. No problems there I understand that, BUT what I can't figure out is will that setup be considered to be equivalent to a " 15 KVA 3 phase" transformer, or a "45 KVA 3 phase" transformer.. I am just curious because if its going to behave like a " 15 KVA 3 phase " transformer, I believe its dangerously overloaded. If its going to be behaving like a "45 KVA 3 phase" transformer, all will be well as far as loading, the only thing that may be wrong would be a code violation regarding the secondary conductor size. He hasn't had any problems as of yet BUT last time I was there he just parked a small rooftop A/C up top and I want to know what I have to work with as far as what actual "size" his transformer bank really is before I hook anything up! ("small rooftop" being 20 amp @ 208V SINGLE phase)..

Thank you for any help anyone can provide!

A.D
Reply With Quote
  #2 (permalink)  
Old 03-09-2005, 06:57 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
All three transformers will be sharing the same load so the rating overall is a 15KVa even with three connected in that configuration. I'd have to consult a transformer book to determine the proper loading and what to expect from the installation. I'll look into it and repost to this thread.
Reply With Quote
  #3 (permalink)  
Old 03-11-2005, 04:19 PM
Handyman
 
Join Date: Feb 2004
Location: Canada.
Posts: 155
Rewired
Send a message via ICQ to Rewired Send a message via MSN to Rewired
Hello HayZee!
Thank you for the information you have provided! Any more you can will be GREATLY appreciated!

I have a chart for Full load currents of different size transformers, It says a 15 KVA 3 phase is only good for 41.6 A @ 208V... Not really much for driving a machine / welding shop loaded with metalarc lighting in the shop, some tools, baseboard heating in the office , Oh ya, almost forgot the electric stove and dryer !!!![:0]
Reply With Quote
  #4 (permalink)  
Old 03-11-2005, 06:01 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
done some searching and he's what I can up with
kVA Full Load Current - Amperes
Rating 120 Volt 240 Volt 480 Volt 600 Volt
KVa 120 240 480 600
3 8.33 7.22 3.61 2.89
6 16.7 14.4 7.22 5.77
9 25 21.7 10.8 8.66
15 41.6 36.1 18 14.4
30 83.3 72.2 36.1 28.9
37.5 104 90.2 45.1 36.1
45 125 108 54.1 43.3
50 139 120 60.1 48.1
75 208 180 90.2 72.2
Reply With Quote
  #5 (permalink)  
Old 03-11-2005, 06:17 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
Calculations for transformers
1 KVa = 1000 va

You stated he had three 15KVa Xfmrs
15 X 1000 = 15000va

Take your secondary voltage and multiply by 1.732 which is a three phase constant to get voltage

208 X 1/732 = 360.2 volts

15000va divided by 360.2 = 41.363Amps (P divided by E = Amps (I)
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,154
Threads: 6,798
Posts: 28,097
Top Poster: HayZee518 (3,837)
Welcome to our newest member, The zzz Man
» Links

» Online Users: 18
0 members and 18 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 03:38 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0