Outlet Help
In an effort to remove painted over wallpaper over really crumbly plater walls, we ended up drywalling. The original outlets are in the baseboards, which will be replacing. My question is, I would love to move these up onto the wall. Can I attach wire to the existing wire using wire nuts and electrical tape so I have about another foot to move these up onto the wall? Is this a major undertaking or something sort of simple (with basic electrical knowledge)?
|

04-12-2005, 01:00 PM
|
|
|
 |
Master Journeyman
|
|
Join Date: Mar 2004
Location: .
Posts: 799
|
|
It may be difficult now with the drywall up, mainly cause the thickness of the wall now may be wider than the arm spread on an old work box. You may need to cut the drywall out around the area you want to install the old work box into, install the old work box and then patch around the box with joint compound, once dry you can then install a box extender to bring the face of the box out flush with the drywall surface. Here's a couple of links that'll show you how to install an old work box in a plaster and lathe wall and how to connect the receptacles.
http://www.hammerzone.com/archives/e...thick_wall.htm
http://www.hammerzone.com/archives/e...ft/connect.htm
Here's a link to show you the box extenders you'll need.
http://www.aifittings.com/m_9.htm
If you want to install a 3prong receptacle then you'll also need to verify a ground exist in the existing receptacle box and then extend a ground between the metal box and the new box you install. Here's a link that'll show how to test for a ground in your existing box.
http://www.codecheck.com/250_50_commentary.html
Be aware that if you decide to move these receptacles up the wall from the current ones installed in the baseboard. The box that is in the baseboard that this splice is made in must ALWAYS remain accessible, meaning a cover plate can be installed over the box to hide the inside of it, but you CAN NOT cover this box with a piece of baseboard to hide it in the wall. It must always remain accessible.
You should also get your self a good book on electrical household wiring. The Black and Decker book to Homewiring is an excellent resource with lots of pictures and diagrams to teach you the basics.
|

04-12-2005, 01:18 PM
|
|
|
Handyman
|
|
Join Date: Apr 2005
Location: Harrisburg, PA, USA.
Posts: 27
|
|
|
Kactus, I should have typed DECIDED to drywall. It's not up, YET... and I figure if we are going to do it, NOW would be the time.... I will review your post carefully, and see if it's something I can handle with my limited electrical knowledge... Thanks a TON.
|

04-12-2005, 01:55 PM
|
|
|
Handyman
|
|
Join Date: Apr 2005
Location: Harrisburg, PA, USA.
Posts: 27
|
|
|
Actually, What I need to know is more about the WIRING than the box it self. Do I need to run a whole new line to the box, or can I somehow attach an extra foot with wire nuts and tape?
|

04-12-2005, 01:58 PM
|
|
|
Handyman
|
|
Join Date: Apr 2005
Location: Harrisburg, PA, USA.
Posts: 27
|
|
|
Got it. Bookstore, here I come...
It wouldn't be a problem to have an acess panel in the baseboard, because I could get the kind that would blend in...
Thanks.
|

04-12-2005, 05:11 PM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
|
|
|
All splices have to be in an accessible junction box - be it a new one or an existing wall case with a blank cover on it. You just can't splice a chunk of cable onto the existing cable with wirenuts and leave it hanging in midair.
|

04-12-2005, 06:39 PM
|
|
|
 |
Master Journeyman
|
|
Join Date: Mar 2004
Location: .
Posts: 799
|
|
Quote:
|
quote:Actually, What I need to know is more about the WIRING than the box it self. Do I need to run a whole new line to the box, or can I somehow attach an extra foot with wire nuts and tape?
|
You can install a piece of NM cable, either 14-2/G for a 15 amp circuit or a piece of 12-2/G for a 20 amp circuit. You connect one end to the wires in the existing baseboard receptacle box and the other end will be routed into your newly installed old work box and be connected to your new receptacle. Use wirenuts to make the splices. Black to black and white to white.
|

04-14-2005, 07:46 AM
|
|
|
Handyman
|
|
Join Date: Apr 2005
Location: Harrisburg, PA, USA.
Posts: 27
|
|
|
ok... this will REALLY show how stupid I am, but How do I know if it's 15 or 20 amp? Will the same procedure for moving the outlet work for moving a light switch, and a light fixture?
|

04-14-2005, 12:33 PM
|
|
|
 |
Master Journeyman
|
|
Join Date: Mar 2004
Location: .
Posts: 799
|
|
|
Look at the breaker for this circuit, it will have a amperage value on the handle. It will say either 15 or 20. If you have fuses, the fuse will have a number on it also.
You can use that same procedure for switches and lights also, just remember, the origianl junction box that has a splice made in it must always remain accessible.
|

04-14-2005, 01:24 PM
|
|
|
Handyman
|
|
Join Date: Apr 2005
Location: Harrisburg, PA, USA.
Posts: 27
|
|
|
Wonderful. Sorry about the dumb questions. We have a wall, which we are removing to open up a staircase, and OF COURSE, thats where the light switch is.
So, I am totally on the page. I get that you have to have access to the "splice", but just for the sake of curiosity, can I ask WHY? Not arguing, just wondering....
Thanks AGAIN.
|
 |
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 10,154
Threads: 6,798
Posts: 28,097
Top Poster: HayZee518 (3,837)
|
| Welcome to our newest member, The zzz Man |
» Links |
|
» Online Users: 25 |
| 0 members and 25 guests |
| No Members online |
| Most users ever online was 388, 07-01-2007 at 02:54 AM. |
|