Putting an outdoor outlet on a free standing patio

My husband and I recently built a free standing concrete patio with a gazebo and I would love to have electric out there. I figured we would run the electric from the garage which is about 25 ft away. The only problem is I have no idea how to accomplish this, any advice is appreciated ! Thanks


Reply With Quote
  #2 (permalink)  
Old 04-18-2005, 01:47 PM
LazyPup's Avatar
Deity
 
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,211
LazyPup is on a distinguished road
You did not state whether you have a load panel in the garage or not, but either way it is about the same.

For a single 15amp duplex outlet you could run AWG 14 wire but for the few pennies difference in wire cost I would prefer to use AWG 12.

12/2 WG type UF romex (type UF=underground feeder) is suitable for direct burial.

I would begin by digging a trench from the point where the wire will exit the garage to the point of demand at the patio, digging the trench at least 6" deeper than your average frost level.

On the patio end I would set a post from the bottom of the trench up to the height were you desire the outlet.

Install a PVC weatherproof outlet box with covers on the post and run conduit down the post until it is at least 12" below grade.

If your soil is rocky i would suggest backfilling a few inches of sand on the wire to pad it before backfilling the soil.

On the garage end I would then run another lenght of conduit from the trench up the garage wall to the point where you are passing the wire through the wall.

Install a pull type elbow on the top of the conduit and a short length of conduit as a sleeve through the wall.

After you begin backfilling you should run a strip of yellow plastic marker tape about a foot underground and parallel to the wire to warn people in future that their is a buried wire there. (You can get the marker tape at all hardwarestores or home supply stores.)

If you have a load panel in the garage that has provision for another breaker you could install a 15A GFCI breaker to feed the run.

If you do not have a load panel you should be able to tie it into the general lighting outlet circuit in the garage but make sure the garage circuit is GFCI protected.

Reply With Quote
  #3 (permalink)  
Old 04-25-2005, 11:54 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
Sure just get a double hub pvc box - one opening in each end and continue the conduit run underground as lazypup has shown you.
Reply With Quote
  #4 (permalink)  
Old 04-26-2005, 05:39 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
Reply With Quote
  #5 (permalink)  
Old 04-26-2005, 11:27 AM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
kactuskid is on a distinguished road
You need to make sure that the cable or conduit used is buried the proper depths and that the circuit is GFCI protected at the receptacles. Here's a link that'll give you lots of details.

http://popularmechanics.com/home_imp...er/index.phtml
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,154
Threads: 6,798
Posts: 28,097
Top Poster: HayZee518 (3,837)
Welcome to our newest member, The zzz Man
» Links

» Online Users: 25
0 members and 25 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 05:00 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0