20 amp circuit blows on 220 pump
I have an irrigation pump that runs off a pressure switch. There is a subpanel about 4 feet from the pump. The pump is listed as 220 20 amp. The sub panel has a 20 amp breaker. The sub panel is fed from the house main panel where there is a 20 amp breaker. The breaker at the sub panel clicks off every few days. The main panel never clicks off. The wire run is 8 guage for about 100 feet. No loose wires have been found.
Choices:
1. 20 amp sub panel breaker is not accurate. (brand new) Replace
2. Replace sub panel breaker with larger amp.
3. Pressure switch is activating the pump too often. There is a 200 gal bladder tank next to the switch. (New switch also)
Any other ideas?
Jerry
|

05-26-2005, 06:00 PM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
|
|
|
Any motor that starts from stop to full speed theoretically is a dead short. If this motor is started and stopped frequently eventually the breaker will trip.
Are the bearings of the motor well lubricated? Is the pump free to turn? Water lubed pump bearings?
If you have access to a clamp around ammeter take a reading when the pump starts and when it is running.
You'll find the amperage on start is about 150% of the nameplate rating.
Is there a motor starter in the circuit? If so check the motor heater elements. Maybe they're too small or too big. Should be the nameplate motor amps. The heater elements of the starter makes up for the initial starting current, if current draw is constant enough the heaters heat up and trip the effected line.
|

05-27-2005, 09:35 AM
|
|
|
New Member
|
|
Join Date: Nov 2004
Location: .
Posts: 22
|
|
|
My neighbor has an amp guage that I will try. It does start and stop as the sprinklers run the pressure down. The motor is about 4 years old and has no visable lube fittings. It is a Gould pool pump, 2 HP. I will check the amp pull.
Thanks
Jerry
|

05-27-2005, 10:03 PM
|
|
|
 |
Handyman
|
|
Join Date: May 2005
Location: San Diego, CA, USA.
Posts: 136
|
|
|
Is the 20 amps listed on the motor referred to as starting current or full load current? A 20 amp FLA motor should be on a 30 amp circuit. A 20 amp circuit is woefully undersized for that load.
|

05-28-2005, 12:48 AM
|
|
|
 |
Deity
|
|
Join Date: Apr 2004
Location: Sharon, PA, USA.
Posts: 2,211
|
|
|
Is the piping properly matched for the pump specifications? A pump is rated to move a specified Gal/min flow at a specified dynamic head pressure. If the discharge line from the pump is too small, or as in the case of an irrigation system, if the irrigation heads are not sized correctly that would increase the dynamic head pressure of the pump, which would result in an increased amp draw.
As Hazee stated, the only way to be sure the pump is running at its rated load would be to take an amp reading while the pump is under load.
Also, if it is a capacitor run 220v motor both the run winding and capacitor winding are supplying power so you must take the amp reading on the common wire to get an accurate reading of the combined feeds.
|

05-29-2005, 07:45 AM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
|
|
|
Because the pump is going on - off so often I can just imagine what the pressure switch contacts look like. Have you considered installing a magnetic starter into the circuit? The starter will protect the motor as it has motor heater elements in the start circuits, and the breaker feeding the circuit exhibits overload protection and short circuit protection. Think of the starter as a sacrificial unit between the source ( breaker ) and the load (motor)
|

05-30-2005, 06:24 AM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
|
|
Here is a pictorial on how to hitch up a contactor (magnetic starter) for the pump motor. A 30 amp sized starter will be sufficient. The heater elements are sized according to motor nameplate FLA data Slightly over is better than undersized.
The coil is rated 240 volt 60 cycle and the circuit uses the available 240 for the control circuit.
[^]
|

06-02-2005, 06:40 PM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
|
|
|
yes
|

06-03-2005, 04:59 AM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
|
|
|
Yes same thing - if I can blow up the pix and incorporate it into a drawing on how to wire it I'll do that.
|
 |
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 10,154
Threads: 6,798
Posts: 28,097
Top Poster: HayZee518 (3,837)
|
| Welcome to our newest member, The zzz Man |
» Links |
|
» Online Users: 21 |
| 0 members and 21 guests |
| No Members online |
| Most users ever online was 388, 07-01-2007 at 02:54 AM. |
|