Remote Sub-Panel

I need to run a 220vac (hot-neutral-hot) and 4 or 6 110vac lines from the main breaker box to a bedroom that I am remodeling. I bought a sub-panel box & connected it to a main breaker on the main breaker box, and was planning to run a handful of 14-2 Romex cables back to the bedroom.

Instead of a bunch of small wires, can I run a big wire from the main breaker back to a sub-panel box in the back bedroom, and use short runs from the subpanel to the bit&pieces?

If this works with code, it would decrease my wiring cost, & decrease the power lost in the wiring during non-peak use times, but I don't know if this is ok with code & such.

Thoughts??

Thanks!!
Reply With Quote
  #2 (permalink)  
Old 06-08-2005, 09:33 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
You can run a sub panel anywhere you want as long as you don't install it in a closet or a bathroom. What size breaker will be feeding the sub-panel? 30 amp 10/4 romex, 40 amp - 8/4 romex, 60 amp - 6/4 romex, 100 amp - 2/4 SER (SER means Service Entrance Round)
Reply With Quote
  #3 (permalink)  
Old 06-09-2005, 02:00 AM
New Member
 
Join Date: Jun 2005
Location: .
Posts: 3
elson
Thanks!!

Couple of questions:

1) Why 4-conductor? 3-conductor plus ground?

2) I have about a 150ft run to the sub-panel. Using some calculators I found on the web, I get #4 wire for 60A. You mentioned #6. Is that fora shorter run, or am I just being too conservative?

Bonus round :-) --- Any idea where to find cheap 3-4 plus ground wire?

Thanks!!! I really appreciate the help!
Reply With Quote
  #4 (permalink)  
Old 06-09-2005, 07:14 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
Attached is a diagram showing you the installation. The fourth wire is for an auxillary ground bar that goes into the sub-panel. The neutral strip in the sub is isolated above ground (no bonding jumper or screw)
The calculator I found for voltage drop is: www.elec-toolbox.com/calculators/voltdrop.htm

Reply With Quote
  #5 (permalink)  
Old 06-09-2005, 02:05 PM
New Member
 
Join Date: Jun 2005
Location: .
Posts: 3
elson
Cool!

So I'm connecting:

Main Sub
---- ---
Hot1 --- Hot1
Hot2 --- Hot2
Neu --- Neu
GND --- GND

Neutral is tied to ground & the panel at the main panel.
At the sub-panel, neutral is NOT tied to ground (to avoid carrying neutral current in the ground conductor), and ground is connected to the subpanel case ground (as normal). The ground wire in the cable can be uninsulated.

I really appreciate your help! I hadn't thought about isolating neutral from ground at the sub-panel, but it is obvious once you mention it :-).

Now to find 150ft of #6-3 grounded cable....

thanks!!!
Reply With Quote
  #6 (permalink)  
Old 06-21-2005, 05:24 PM
New Member
 
Join Date: Jun 2005
Location: .
Posts: 1
camarojweed
I also wanted to post here with some questions to make sure my thoughts are right on this.

I have my subpanel installed in my basement and am looking over the wiring now before I make any connections.

I am installing a 100amp breaker in the main panel that runs to a main lug sub. I am using 2/4 wire and the run is about 35 feet.

I noticed as mentioned above that the ground and neutral are combined in my main panel. Is it correct to connect both wires in my main panel (ground and neutral) to the same lug and just make sure they are separate in my subpanel?

Thanks

Jason

also if you could send that 60 amp picture to my email that would be great so I could get a more clear look at it.

camarojweed@comcast.net
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,154
Threads: 6,798
Posts: 28,097
Top Poster: HayZee518 (3,837)
Welcome to our newest member, The zzz Man
» Links

» Online Users: 19
0 members and 19 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 04:16 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0