Converting 2 prong to 3 prong

About 1/3 of my house still has the 2 prong outlets in it. Should I change them to the 3 prong self grounding outlets or keep them? Just wondering about the safety of the 2 prong and the 3 prong self grounding.
Also what is the difference between a 3 prong grounding and a 3 prong self grounding?
Thanks all.
__________________
Jtfoxman
Reply With Quote
  #2 (permalink)  
Old 02-22-2006, 09:07 PM
Handyman
 
Join Date: Jan 2006
Posts: 157
Phelps is on a distinguished road
I have never heard of a self grounding outlet before. That is a new one on me, and I hope someone else comes on here.

Regarding what is code, I believe it is okay that if you have 2 wires only, that as long as you use 2-prong plugs (they cost me $1.25 ea instead of the 44 cent for the 3-prong jobbies), in areas that normally don't require a ground ...say in the living room or bedrooms that are just going to be using 2-prong plugs (no computer), that this would be fine. I know that our local inspectors approve this when houses I maintain get inspected. And THEY are fussy!
Reply With Quote
  #3 (permalink)  
Old 02-23-2006, 10:08 AM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
kactuskid is on a distinguished road
In order to install a 3 prong receptacle you MUST have a ground in the box, otherwise you can install a GFCI receptacle. This will provide a 3 prong plug but still will not provide a ground.

If the cable that supplies power to the receptacle box is armored cable then a ground MAY exist in the box. To tell you need to buy a neon bulb voltage tester or a multimeter. You measure between the hot wire and the metal box. If you get either 120 volts or a light on the tester then this indicates a ground is present in the box. Then you can install a 3 prong self grounding receptacle in place of the 2 prong. Self grounding receptacles are sold at Home Depot and indicated on the box to be self grounding. If you want to install a regular 3 prong receptacle and not the self grounding type, then you must pigtail a ground wire to the box using a 10-32 screw.

Your other option is to run a new circuit to the living room that has a ground and install a new 3 prong receptacle.

Here's a link that'll explain all of this to you and under what conditions you can replace a 2 prong with a 3 prong.

http://www.codecheck.com/250_50_commentary.html

A self grounding receptacle has a special clip on the yoke and will look like this:


They don't require a pigtail ground wire be installed to the metal box. But, like said above, you are not allowed to install a 3 prong receptacle in place of a 2 prong unless the box is grounded. Your existing 2 prong receptacles are fine to use unless you want to run a device that requires a ground, such as a computer.
Reply With Quote
  #4 (permalink)  
Old 02-23-2006, 01:04 PM
Handyman
 
Join Date: Jan 2005
Location: Hazleton, PA, USA.
Posts: 62
jtfoxman
Thanks for the quick reply!
__________________
Jtfoxman
Reply With Quote
  #5 (permalink)  
Old 02-23-2006, 10:41 PM
Handyman
 
Join Date: Jan 2005
Location: Hazleton, PA, USA.
Posts: 62
jtfoxman
Well I went ahead and tested the outlets. I get a constant 120v when I touch the black wire and the box. So I am going to go ahead and purchase the self-grounding outlets. I was surprised that the boxes were grounded since I don't see any metal wire cables in my basement or behind the outlets. They wire just looks like the older cable that has a cloth like outer cover.
__________________
Jtfoxman
Reply With Quote
  #6 (permalink)  
Old 02-24-2006, 12:18 AM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
kactuskid is on a distinguished road
Hmmm, you need to hold off installing those 3 prong receptacles until this can be figured out. If you have the older cloth romex with no ground wire, then you may not really have a ground. But wierd that you would read the voltage then.

Are there any other wires in this box that are connected to the box or making contact with it? Did you disconnect the wires from the receptacle, spread them apart and then take your reading? If you just measured from the front of the receptacle to the box, then it's possible that you may have a bootleg ground somewhere in that box or on the circuit. This is where a ground and the neutral are bonded together on the load side of your electrical service panel and it is very dangerous and can give a false reading of having a ground.

One way to know for sure if you have a bootleg ground is to connect a GFCI receptacle to the wires in the box. The GFCI will sense a ground fault and will trip if anythings plugged into it.

Last edited by kactuskid; 02-24-2006 at 12:41 AM.
Reply With Quote
  #7 (permalink)  
Old 02-24-2006, 07:14 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
What you are seeing in the box is the jute fiber that surrounds the conductors "inside" the bx covering. Newer Bx used a paper wrap instead of the fiber. The jute fiber has a waxy feel to it when you strip off a length of the armor.
Reply With Quote
  #8 (permalink)  
Old 02-24-2006, 07:34 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
New Bx - Old Bx

Here's what the old vs the new Bx looks like. In the jute fiber type there may be a blue or red thread along with the tannish jute fiber.
Attached Images
File Type: jpg bx.JPG (20.0 KB, 21 views)
Reply With Quote
  #9 (permalink)  
Old 02-24-2006, 10:18 AM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
kactuskid is on a distinguished road
Aaah, I'm betting Hazy is right on. You won't see the armored cable from inside the box, only the old wires sticking out of it. When you said you couldn't see it behind the outlets I figured you had access to see the connection from an open cavity in the wall.

And older homes didn't have the wiring run through the basement. It was always run up through the attic and down into the wall studs to the receptalces, usually from the light fixtures which served as the junction boxs.

Course if these receptacles are supplied via Knob and Tube wires then that's a different story.
Reply With Quote
  #10 (permalink)  
Old 02-24-2006, 04:51 PM
Handyman
 
Join Date: Jan 2005
Location: Hazleton, PA, USA.
Posts: 62
jtfoxman
I looked into the outlet box again and I could see what is coming into the box. It isn't no bx cable. The wires are wrapped in a paper material and that is covered with black insulation and what looks like then it was covered in silver substance, like paint. No other wires in the box.
I checked the main breaker then and there is no bx cable running from that either. I took the cover off and it looked like there was a few connections that had the ground and the white wire together. Is this what you called bonding. Can I just kill the power and unbond them and place the ground in another open spot? Can I put 2 grounds in the same open slot?
__________________
Jtfoxman
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,154
Threads: 6,798
Posts: 28,097
Top Poster: HayZee518 (3,837)
Welcome to our newest member, The zzz Man
» Links

» Online Users: 27
0 members and 27 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 04:35 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0