Replacing Stove Top with Range

We are remodeling and will be changing out our stove top with a range. The current wiring is bx cable with one red, one black and one white wire. The current breaker is 2 - 2 pole 30 amp breakers. The installation manual states "You must us a 3-wire, single-phase A.C. 208Y/120 Volt or 240/120 Volt, 60 hertz electrical system." The appliance store sold us a 3 pole -4 wire surface mount range outlet (requiring 2 hot wires, one neutral and one ground) and a 4 wire range power cord. Will we be able to utilize the existing wiring for the new range or should we just run new from the box?
Reply With Quote
  #2 (permalink)  
Old 02-23-2006, 04:14 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,837
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
New installations require by code the 4 wire plug and receptacle. Also the older ranges or stove tops only needed 30 amps. Most ranges need a minimum of 65 amps 6/4 cable.
Reply With Quote
  #3 (permalink)  
Old 02-23-2006, 05:16 PM
New Member
 
Join Date: Feb 2006
Posts: 2
the.vicster is on a distinguished road
Thanks for answering. I guess we'll just run all new. I figured that's what we'd have to do. I was looking for an easy out.
Reply With Quote
  #4 (permalink)  
Old 02-25-2006, 06:32 AM
Handyman
 
Join Date: Sep 2004
Location: Aliso Viejo, CA..
Posts: 129
Snoonyb
Appliance wiring

Quote:
Originally Posted by the.vicster
Thanks for answering. I guess we'll just run all new. I figured that's what we'd have to do. I was looking for an easy out.
Just a minute
Before you arbitraily re-wire, first determine the load so that you can properly size the run, if its needed.
From the same nomenclatue information will also be a power requirement stated in watts, such as 7KW or 7000 watts. You divide this value by the voltage you have available and this will then determine the operating current of the appliance.
To size the breaker and wire you add 20% to the operating current.

Should it turn out that your existing wire and breaker will work, the red and black are the two hot conductors, the white is the neutral and since your run is in BX the metalic casing acts as the ground. There needs to be a metal box at the appliance recepticle location to which you attach a conductor from the new recepticle grond terminal, to the bonding screw in the box.
__________________
Illegitimas non-carborundum
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,154
Threads: 6,798
Posts: 28,097
Top Poster: HayZee518 (3,837)
Welcome to our newest member, The zzz Man
» Links

» Online Users: 27
0 members and 27 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 04:34 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0