running power to a detached garage in NW Indiana

This summer, I plan on running power out to my detached garage.

Conditions: All season weather upper midwest USA. Distance run is about 60 feet. 120 VAC, have not sized current rating yet, lets say 75 Amp as an estimate.

Underground seems more appealing to the eye then overhead and easier to install. From a safety stand point, is underground the way to go also? Or maybe a better question is, what limitations and or liabilities does underground have-if any?

Also, I intend on pouring a sidewalk between the house and the garage. Would i run the conduit next to the sidewalk or under it?

How deep in the ground should the conduit be? For example does it need to be below some type of frost-line?

Thank you.
Reply With Quote
  #2 (permalink)  
Old 03-06-2006, 11:09 PM
Handyman
 
Join Date: Sep 2004
Location: Aliso Viejo, CA..
Posts: 129
Snoonyb
The sidewalk is your choice to locate.
Yes you need to be below the frost line.
__________________
Illegitimas non-carborundum
Reply With Quote
  #3 (permalink)  
Old 03-07-2006, 08:38 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,838
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
For a one way run of 120 volts to a 75 amp load would require THREE #4 cables in a conduit. The conduit would be a 1 1/4 or 1 1/2 inch diameter. Easier way would be to run 240 volts to the garage, the conductor size would be reduced as well as the conduit size. At 240 volt 75 amp - would need 4 #8 conductors to a sub panel.
Cost of fittings would be cheaper too. In either case an expansion sleeve is needed at one end of the run.
Reply With Quote
  #4 (permalink)  
Old 03-07-2006, 07:17 PM
wak wak is offline
Handyman
 
Join Date: Feb 2006
Posts: 33
wak is on a distinguished road
Hayzee,

let me see if I understand this correctly, please. Your saying to run the 240 because more voltage equates to less current per ohms law.

I would then wire up the single phase 240 as as 120 in the garage. hence the other advantage is if I have a 240 vac air compressor I can plug in as well in a 240 outlet.

Is this correct?

Also what is the considered frost line depth in my part of the country near Chicago?

thanks

Last edited by wak; 03-08-2006 at 12:09 AM.
Reply With Quote
  #5 (permalink)  
Old 03-08-2006, 12:34 AM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
kactuskid is on a distinguished road
To help make things more clear, you basically have two choices. You can run a single 120v 20 amp circuit to your garage or you can run a 240 volt service to your garage which would then require a subpanel installation in the garage. This subpanel would then provide numerous 120 volt circuits and 240 volt circuits to supply power for your needs.

And the cable does not need to be buried below the frost line. Since you are in Chicagoland where NM-B cable is not allowed then you probably can't install UF cable either. You'll need to install PVC conduit and run THHN/THWN wires inside, and it would need to be buried 18".

Underground is the way to go here, just make sure you call Miss Dig or Diggers Hotline so they can flag all your utilities first so you don't hit anything.

I would not suggest running the conduit under the sidewalk if you have a choice. Much easier to dig up the conduit if ever need be. And all receptacles in your garage must be GFCI protected. Here's a link that'll show you how to run a single 20 amp circuit to your garage, a 240 volt circuit would be a bit different in that the conduit would terminate to a subpanel instead of a j-box.

http://www.popularmechanics.com/home...t/1275601.html

Last edited by kactuskid; 03-08-2006 at 12:40 AM.
Reply With Quote
  #6 (permalink)  
Old 03-10-2006, 12:12 AM
wak wak is offline
Handyman
 
Join Date: Feb 2006
Posts: 33
wak is on a distinguished road
The 240 vac to a sub panel sounds perfect. Spring is almost here and the projects are pileing up.
That Popular Mechanics article is really good, would be a good idea to post that under illustrations.


Thanks guys!

Last edited by wak; 03-10-2006 at 12:14 AM.
Reply With Quote
  #7 (permalink)  
Old 03-10-2006, 01:26 PM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
kactuskid is on a distinguished road
If you're gonna install a subpanel at the garage then you're gonna need more instructions than just that previous link. The conduit and wire sizes will be different depending on the size of service you want out there. A 60 amp service should be more than enough unless you're gonna run a ton of things at once.

Go to this link: http://www.selfhelpandmore.com/homew...rage/index.htm and on the left hand side scroll down to where it says:

"PICTORIAL EXAMPLE OF A GARAGE PANEL WITH 3 OR MORE CIRCUITS 240 VOLT 60 AMP, 100 AMP, 200 AMP BRANCH CIRCUIT WITH UNDERGROUND CONDUCTORS WITH AN EQUIPMENT GROUNDING CONDUCTOR RAN WITH THE FEEDER SUPPLYING THE DETACHED STRUCTURE"

It will explain to you that you also need to install a ground rod at the garage along with other pertenent details.
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,154
Threads: 6,798
Posts: 28,098
Top Poster: HayZee518 (3,838)
Welcome to our newest member, The zzz Man
» Links

» Online Users: 47
0 members and 47 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 08:51 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0