Detached Garage Grounding - Do I install another ground rod or run 4 #4s from my main

I have two stories. 1 Electrician telling me I need to install a grounding rod next to my detached garage and run 3 #4s back to my main panel.

2nd electrician telling me to run 4 #4s back to my main panel.

which one is correct?

Also what size conduit would you use?

thx guys!!
Reply With Quote
  #2 (permalink)  
Old 03-23-2006, 08:55 PM
pushkins's Avatar
Handy, Man
 
Join Date: Mar 2006
Location: North Carolina
Posts: 492
pushkins is on a distinguished road
I just finished a month or so a garage panel install for my own detached garage with a 60 amp panel. Code here says that all detached structures with panels MUST be grounded by means of a grounding rod and #6 solid ground.
As for the grounding back to the main board again here with my 60 amp garage panel I had to run a #6 ground wire back to the main panel.

In regards to your conduit question it will depend on just how many wires you need run back (why more than one return ground I don't know). I have attached a conduit calc. for you just fill in the blanks and it will give you the code sizes calcs.

http://www.electrician.com/calculato...lc_rev0326.htm
Reply With Quote
  #3 (permalink)  
Old 03-24-2006, 04:17 AM
Handyman
 
Join Date: Sep 2004
Location: Aliso Viejo, CA..
Posts: 129
Snoonyb
The second. Plus the ground rod, with the #6 armored.
__________________
Illegitimas non-carborundum
Reply With Quote
  #4 (permalink)  
Old 03-25-2006, 10:43 AM
New Member
 
Join Date: Mar 2006
Posts: 3
robsatx is on a distinguished road
....

Will a number the # 4 work in lieu of the # 6? I already bought a 500 foot spool. Guess I could take it back.

BTW thanks for the replys!!!!
Reply With Quote
  #5 (permalink)  
Old 03-25-2006, 01:02 PM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
kactuskid is on a distinguished road
You definatly want to run 4 wires plus install a ground rod. The #6 ground wire is important cause the ground kit on the panel won't accept a #4 wire, but, you can purchase a connector to accomidate the #4. It connects to the ground bar. What is the make/model of panel you're installing?

And there are also important rules when installing a subpanel, like making sure you throw away the green bonding screw so the ground and the neutral buss bars are separted.

Here's a link that'll show you what is required based on your particular situation. Scroll down on the left side of the link for diagrams as well.

http://www.selfhelpandmore.com/homew...rage/index.htm

Last edited by kactuskid; 03-25-2006 at 01:06 PM.
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,154
Threads: 6,798
Posts: 28,098
Top Poster: HayZee518 (3,838)
Welcome to our newest member, The zzz Man
» Links

» Online Users: 43
0 members and 43 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 08:26 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0