04-27-2006, 09:23 PM
|
|
|
New Member
|
|
Join Date: Apr 2006
Posts: 4
|
|
Breaker popping
Hi All. New here. My 20amp circuit breaker for my garage keeps popping. "NOTHING" is on. WHY! Last Saturday/Sunday we had rain, pretty heavy. Nothing new here in the Northeast. Breaker has been fine all week. This just started today. My thinking is that the breaker is shot. Anyone else have ideas? 
|

04-27-2006, 09:36 PM
|
|
|
 |
Moderator
|
|
Join Date: Jul 2002
Location: USA.
Posts: 529
|
|
|
You could try switching the breaker with another 20 amp in the box and see if the problem follows the breaker. If it does, then replace it.
Welcome to the forum!
__________________
Tr  y
|

04-27-2006, 09:42 PM
|
|
|
New Member
|
|
Join Date: Apr 2006
Posts: 4
|
|
try it
One more question. Certainly not a electrician here. So I don't make my hair  stand up  . Can I turn the main switch off in the panal, and switch breakers?
|

04-27-2006, 10:05 PM
|
|
|
Handyman
|
|
Join Date: Sep 2004
Location: Aliso Viejo, CA..
Posts: 129
|
|
|
Is the run to your garage under ground, in metal, in plastic, in conduit, in romex and how many conductors?
__________________
Illegitimas non-carborundum
|

04-27-2006, 10:15 PM
|
|
|
New Member
|
|
Join Date: Apr 2006
Posts: 4
|
|
wiring
It is underground in conduit w/ romex. Sorry forgot to mention this. Then it goes into a panal/box w/ on/off switches.
|

04-28-2006, 04:05 AM
|
|
|
Handyman
|
|
Join Date: Sep 2004
Location: Aliso Viejo, CA..
Posts: 129
|
|
|
You probably have water in the conduit which has caused a deterioration in the wire insulation and a subsequent short.
Since you are also probably unfamiliar with working behind a "dead front panel", absolutly turn the power off at the main before you attempt anything inside the electrical service.
You can test this by using another breaker in the panel, however, everytime a breaker fails because of an electrical problem in the connected circuit, the devise is weakened, and its useful life shortened.
You'll need an inexpensive VOM (Voltage, Ohm meter).
To check the breaker;
1) With the MAIN disconnect turned off and the breaker in question turned off, not failed, remove and seperate the conductor from the side of the breaker.
Reset the breaker to the on position and turn the MAIN service disconnect on.
2) With the meter in the voltage scale and the range set to a scale higher than 200V, test for the presence of voltage at the screw on the breaker to the neutral buss bar.
If voltage is present (120V), the breaker is working.
To check for a short;
1) With the main service diconnect turned off.
2) Turn off the breaker in question and test for the presence of voltage at that breaker.
3) Disconnect the conductor from the breaker, the corresponding white or neutral conductor from the neutral buss bar and if there is one , the ground conductor, seperate.
4) In the garage, open the "J" box, disconnect and seperate the incoming conductors.
5) With the meter set on the Ohm scale test all of the conductors to the conduit,DO NOT, use your fingers to pinch the conductors to the meter probs.
6) Next, with the meter still on the Ohms scale, test the colored and white conductors to the ground conductor and then to each other.
If there is a reading from the colored or white conductor, either to each other and/or to the ground and/or conduit, you have a short.
__________________
Illegitimas non-carborundum
|

04-28-2006, 08:46 AM
|
|
|
New Member
|
|
Join Date: Apr 2006
Posts: 4
|
|
|
thanks
thank You Snoonyb.
|

04-28-2006, 02:01 PM
|
|
|
 |
Master Journeyman
|
|
Join Date: Mar 2004
Location: .
Posts: 799
|
|
|
What is the color of the outer insulating sheathing of the romex? Is it white or yellow? Romex is not recommended to be installed in conduit if the run is closed off at both ends, and, any romex installed in the ground needs to be UF type. Regular NM-B cable (romex) is not rated for wet areas. The wiring installed in the conduit, (and it should be plastic conduit,) need to be single wires that are rated THHN/THWN. If anything other than these rated wires or UF cable is installed then it'll rust through and break.
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 10,154
Threads: 6,798
Posts: 28,098
Top Poster: HayZee518 (3,838)
|
| Welcome to our newest member, The zzz Man |
» Links |
|
» Online Users: 32 |
| 0 members and 32 guests |
| No Members online |
| Most users ever online was 388, 07-01-2007 at 02:54 AM. |
|