Patio Wiring under concrete...

Hi,
I would like to run about 12' of new wire from an exitising outdoor outlet (GFCI) mounted on a fence made of cinder blocks, to a new outlet (GFCI) under a current concrete slab that would be located under our patio table for rope lighting the umbrella, ect. I would have to cut a stip of concrete out to lay the new wire. I do understand that the GFCI Box would need to be mounted at least 1' off the ground, and we do have an inground swimming pool about 15-20 feet away. My queston is how deep should I cut through the concrete, and what kind on wire should I use. Also would I run the new wire through piping like conduit or PVC under the concrete slab?
Any other tips would be greatly apreciated!

Thank You!
Rod
Reply With Quote
  #2 (permalink)  
Old 04-28-2006, 10:59 PM
pushkins's Avatar
Handy, Man
 
Join Date: Mar 2006
Location: North Carolina
Posts: 492
pushkins is on a distinguished road
For most 4" thick slabs you have to cut all the way through them and then dig down 8", lay 1/2" or 3/4" conduit and run underground cable inside this conduit.
The cable must be suited for wet locations, as inside conduit is still clased as a wet location (humidity etc...)

You could also cut the slab, dig down 18" and direct bury cable (suited for direct bury) but you still have to run conduit from the 18" depth upwards to 12" out of grade to house the wire.
Reply With Quote
  #3 (permalink)  
Old 04-29-2006, 08:00 AM
Handyman
 
Join Date: Sep 2004
Location: Aliso Viejo, CA..
Posts: 129
Snoonyb
Cut the concrete just slightly wider then the width of a plumbers trenching shovel.
Conyact your local building authority regarding the required trench depth conduit and direct buriel application.
In some jurisdictions, mine in praticular. When using plastic conduit, the sweep and verticle riser must be metalic pipe.
This also applies to direct burial, in that it must be sleeved.

ENCASING ROMEX OF ANY KIND, IN CONDUIT, OF ANY KIND, IS EXPRESSLY PROHIBITED.
__________________
Illegitimas non-carborundum
Reply With Quote
  #4 (permalink)  
Old 05-02-2006, 06:54 PM
New Member
 
Join Date: Feb 2006
Posts: 2
sutter_county is on a distinguished road
Thanks for your help!

I didn't think I would have to dig that deep. I'll have to see if I can get some dynamite from Craigslist to make the job easier.
Thanks for your input.
Rod
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,154
Threads: 6,798
Posts: 28,098
Top Poster: HayZee518 (3,838)
Welcome to our newest member, The zzz Man
» Links

» Online Users: 44
0 members and 44 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 09:22 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0