Had a home inspection done. Here are 2 things i want to fix. The sub-panel in my garage has the ground and neutral wires both attached to the neutral bus bar. I know the ground wire must be removed but what do i do with it? There is no ground bus bar in the panel.
|
You need to install a ground bar then. You can buy them for your particular panel, there should be holes in the back of the panel that the ground bar screws will line up with. Go to an electrical supply house for a better selection. Beaware that the existing neutral bar must float above the metal panel and not be of the same continuity.
Quote:
|
Next question- The garage sub-panel has fuses. The wire run through the garage is 12/2. Two circuits have 15 amp fuses. The other circuit with two lines running out of it has a 30 amp fuse. What size fuses should i be using.
|
A 12/2 wire gauge can be protected by a 20 amp fuse. A 14/2 wire gauge can be protected by a 15 amp fuse. If the supply wire to the garage sub panel is 12/2-g then you cannot use a fuse larger than a 20 amp.