PeruvianHighlander
Question Grounding for Three-Prong 220v Outlet

I need to add a three-prong 220 volt outlet for a dryer. I did a lot of research to figure out what I needed, so I bought an outlet, 10-3 cable, and a bi-pole 30 Amp breaker. Once I got it home, I opened up the outlet and it has only three screws: one silver for the nuetral wire, and two copper for the hot wires, but no green one for the ground!
On the back of the bag it says this:
CAUTION: This device is not for grounding use. Connect only to non-grounding circuits unless it is to be used for range or clothes dryer in accordance with the National Electrical Code.

I am using this for a dryer, so it should be grounded, correct? Did I get the wrong outlet? This was the only outlet they had at Lowe's:
http://www.lowes.com/lowes/lkn?actio...dryer%20outlet

It is the middle item in the link above. Please help me if you can tell me how to wire this outlet, or if I need something different. Thank you.
Reply With Quote
  #2 (permalink)  
Old 08-02-2006, 10:56 PM
Handyman
 
Join Date: Sep 2004
Location: Aliso Viejo, CA..
Posts: 129
Snoonyb
Does your existing appliance cord mate to this recepticle?
__________________
Illegitimas non-carborundum
Reply With Quote
  #3 (permalink)  
Old 08-03-2006, 12:59 AM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
kactuskid is on a distinguished road
All new dryer circuits MUST be of the grounded type no matter what your existing dryer's cord configuration is. The proper cable MUST contain a ground wire so I hope you really purchased 10-3/G. The 3 slot receptacle you purchased is the wrong one.

You need to buy a NEMA 14-30 receptacle that has 4 slots in it like this one:

http://www.foxelectricsupply.com/con...ductNo=EAG1225

If Lowes doesn't carry it then go to a good hardware store like Ace or True Value but per your link the PROPER one is on the far left.

Then use the following link to wire it up and also make sure you have a 4 prong cord connected to the back of the dryer.

http://www.selfhelpandmore.com/switc...ryer/index.htm
Reply With Quote
  #4 (permalink)  
Old 08-03-2006, 08:20 AM
New Member
 
Join Date: Sep 2005
Location: Pittsburgh, PA, USA.
Posts: 4
PeruvianHighlander
Thank you for your responses

To answer SnoonyB's question: yes, my dryer's power cord currently has three-prong configuration that fits the outlet I purchased.

Lowe's has several of the four-prong outlets, but I did not purchase them because my dryer has a three-prong configuration. I saw many posts explaining the process of replacing the cord in the dryer and I think I can take care of that. I did buy 10-3 (Black, White, Red, and ground). Thank you for all of your help. I guess my only questions, are: why would they make ungrounded outlets in the first place (safety)? and why do hardware stores still sell them? Regardless, thank you very much for your help.

PeruvianHighlander

Last edited by PeruvianHighlander; 08-03-2006 at 08:23 AM.
Reply With Quote
  #5 (permalink)  
Old 08-03-2006, 11:37 AM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
kactuskid is on a distinguished road
Quote:
why would they make ungrounded outlets in the first place (safety)? and why do hardware stores still sell them?
Three prong ungrounded receptacles are still made and sold to replace existing broken ones. The old code allowed the circuit neutral wire to also serve as the equipment grounding conductor. These old existing circuits are allowed to be used but cannot be extended. So if one exist in a house and a new dryer is bought that has a 4 prong cord, the dryers cord is allowed to be changed to a 3 prong one to utilize the existing circuit.

But, the code states that any NEW dryer or range circuits MUST BE grounded and therefore require the 4 prong receptacles. This is what you want anyhow cause YES, it is safer than the older 3 prong types.

If you need to also change out your existing 3 prong cord to a 4 prong make sure you remove the existing ground strap that connects the circuit neutral to the dryers frame and that the ground on your 4 prong cord is then connected to the dryers frame. This is all shown and explained in the link above.

Last edited by kactuskid; 08-03-2006 at 11:50 AM.
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,154
Threads: 6,798
Posts: 28,098
Top Poster: HayZee518 (3,838)
Welcome to our newest member, The zzz Man
» Links

» Online Users: 40
0 members and 40 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 08:42 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0