Question 120v off one leg of 220v

I have a 220v circuit (12-2 with ground wire) and would like to make a 120v branch off of one leg and the ground. I also want to keep the 220v circuit live.

Since the 12-2+G 220 circuit will still be in use, I don't have a way to run a neutral back to the panel but will have the ground.

So, 2 questions:
a) Will this work? (Without anyone being in danger!)
b) If yes, how should the 120 branch be wired? Neutral and ground both going to the ground in the 220 feeder circuit?

Thx in advance for any replies. (BTW, I did try to research this using the search link .. some questions/answers were close but not quite the same.)

Another "by the way": I'm in a rural area where "code" doesn't exist and need this branch just for a hookup for an RV.
Reply With Quote
  #2 (permalink)  
Old 09-06-2006, 06:56 PM
Piper's Avatar
Handyman
 
Join Date: Aug 2006
Location: Pennsylvania
Posts: 33
Piper is on a distinguished road
Based on what little information you provided I would say no.

What is the load on the current 220V circuit? Watts or Amp draw

How many feet is it from the breaker box to the 220V load?

What is the load of your rv?

What size breaker feeds the existing Circuit?
Reply With Quote
  #3 (permalink)  
Old 09-06-2006, 09:47 PM
New Member
 
Join Date: Aug 2006
Location: Central TX
Posts: 17
Luv2Q is on a distinguished road
Quote:
Originally Posted by Piper View Post
Based on what little information you provided I would say no.
Your questions in italics, followed by my answers.

What is the load on the current 220V circuit? Watts or Amp draw
Ans: Currently, there's no load on the 220V circuit. Once used for a deepwell pump which is no longer in use.

How many feet is it from the breaker box to the 220V load?
Ans: Approv 75' to the 220 outlet.

What is the load of your rv?
Ans: 120V, 30 Amp

What size breaker feeds the existing Circuit?
Ans: 30 Amp


Thx
Reply With Quote
  #4 (permalink)  
Old 09-06-2006, 11:23 PM
Handyman
 
Join Date: Sep 2004
Location: Aliso Viejo, CA..
Posts: 129
Snoonyb
Quote:
Originally Posted by Luv2Q View Post
Another "by the way": I'm in a rural area where "code" doesn't exist
I'm sure, were you to suffer a loss as the result of to large a breaker for the max. current carrying capability of the conductor, your insurance company would find that refreshing.

Your existing situation is good for A) 20A, 240V, B) an 20A, 120V.

Back to your original.
1) How is this circuit wired?
Is it direct burial?
Is it in PVC?
Is it in metallic piping?
__________________
Illegitimas non-carborundum
Reply With Quote
  #5 (permalink)  
Old 09-07-2006, 01:25 AM
New Member
 
Join Date: Aug 2006
Location: Central TX
Posts: 17
Luv2Q is on a distinguished road
Quote:
Originally Posted by Snoonyb View Post
I'm sure, were you to suffer a loss as the result of to large a breaker for the max. current carrying capability of the conductor, your insurance company would find that refreshing.
No need for sarcasm. I was mentioning the lack of code restrictions in a rural area simply because there are occasions when something that doesn't "meet code" works perfectly well. I'm here to try to get information so that the aforesaid loss doesn't happen. If I were already an expert, I wouldn't be bothering. Thanks for your input.
Reply With Quote
  #6 (permalink)  
Old 09-07-2006, 05:06 AM
Handyman
 
Join Date: Sep 2004
Location: Aliso Viejo, CA..
Posts: 129
Snoonyb
Quote:
Originally Posted by Luv2Q View Post
I'm here to try to get information so that the aforesaid loss doesn't happen. If I were already an expert, I wouldn't be bothering. Thanks for your input.
And information you were provided.

Yet, the solution to your quest may lie in the unanswered question;
"1) How is this circuit wired?
Is it direct burial?
Is it in PVC?
Is it in metallic piping?"
__________________
Illegitimas non-carborundum
Reply With Quote
  #7 (permalink)  
Old 09-07-2006, 12:24 PM
kactuskid's Avatar
Master Journeyman
 
Join Date: Mar 2004
Location: .
Posts: 799
kactuskid is on a distinguished road
What your currently have with the 12 gauge wire being protected by a 30 amp breaker is dangerous as it stands. Max breaker on this gauge wire should be 20 amps to prevent a fire.

And no way can you tap a 110 circuit from the existing 220 amp circuit and utilize them both at the same time. It's either one or the other. If you want a full 30 amps supplied to your RV then you'll have to run new 10 gauge wire, otherwise you can supply a 20 amp circuit utilizing the existing wire.
Reply With Quote
  #8 (permalink)  
Old 09-08-2006, 06:51 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,838
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
I agree totally with kactuskid. If your supply was a three wire with ground, that is a red, black, white and bare ground then you might get 120 off either phase and the white. Again 12/2 needs 20 amp not a 30 amp breaker. You mention that the bare ground goes tothe neutral buss in the main panel. You cannot utilize an equipment grounding conductor to suffice as a neutral.
Reply With Quote
  #9 (permalink)  
Old 09-08-2006, 11:58 AM
OMKEN's Avatar
New Member
 
Join Date: Sep 2006
Location: Maryland
Posts: 4
OMKEN is on a distinguished road
Converting to 120V circuit

You claim that you no longer need the 220V circuit, as the pump is no longer in service. If that is the case, I would simply replace the 2 pole breaker feeding the circuit with a 1P-20A breaker, move the white (neutral) conductor to the neutral bar and you will then have your 120V circuit and the proper rated breaker for the #12 wire.

I understand that you are in a rural "code less" area, but keep in mind that most of the time there are valid safety reasons for adhering to the code.

Good luck !
Reply With Quote
  #10 (permalink)  
Old 09-11-2006, 05:30 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,838
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
Just to add to the "code-less" portion of the thread, if you were to call your building inspector's office I'm sure he can direct you to a UL inspector who will suffice as an electrical inspector. I live in rural New York State where the same is true however there are UL inspectors in the area.
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,154
Threads: 6,798
Posts: 28,098
Top Poster: HayZee518 (3,838)
Welcome to our newest member, The zzz Man
» Links

» Online Users: 42
1 members and 41 guests
Java_Bob
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 09:24 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0