Need a wire reel idea !!!
I am going to pull 2-3o and 2-2o wires into a 3 inch conduit and need to build something to hold onto the wires and un-reel them as I pull. There is 160 feet of wire to pull. Has anyone designed a pull reel that I can build for this job?
Jerry
Eating my Wheaties for this weekend!!
|

09-28-2006, 11:12 PM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,838
|
|
|
Easy job - use a piece of 1 1/2" pipe to go through the reel holes and two saw horses. Use an 1 1/2 Inch one hole strap screwed into each sawhorse.
Use two people when pulling - one to feed the cables and apply wire lubricant, the other operates the tugger. Pull slow and steady. Don't let the cables twist over themselves, try to keep one uniform bundle. if they twist over themselves, stop the pull, pull back, straigten out the cable and resume pulling. You know you have to derate the current capacities where you're pulling 4-6 conductors in a conduit by 80% don't you? Did you calculate the cross sectional area of each conductor and multiply by two, then add them together for the total area? The internal diameter of a conduit has a cross sectional area that can be filled by two percentages of cables.
Last edited by HayZee518; 09-29-2006 at 07:04 AM.
Reason: wrong script
|

09-28-2006, 11:14 PM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,838
|
|
|
What's the insulation type printed on the cable ?? THW, RHH ?
|

10-06-2006, 05:45 PM
|
|
|
New Member
|
|
Join Date: Nov 2004
Location: .
Posts: 22
|
|
|
THHN on the outside of the cables. Turns out the electric supply place did not put the cables on reels so I laid them out on the ground. With my wife pulling (not much), I put a quart of lube down the tube and lifted the wires onto my shoulder and pushed them down the hole. Was not hard at all. Just tiring to lift the wires.
Jerry
|

10-08-2006, 06:22 AM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,838
|
|
|
I agree - wire pulling [or pushing] is not easy - THHN is good, the nylon covering over the TW insulation raises the temperature co-efficient to 90 degrees C. The lubricant you used will over time evaporate out of the pipe and just form a soap powder in the pipe, IDEAL yellow works good.
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 10,154
Threads: 6,798
Posts: 28,098
Top Poster: HayZee518 (3,838)
|
| Welcome to our newest member, The zzz Man |
» Links |
|
» Online Users: 35 |
| 0 members and 35 guests |
| No Members online |
| Most users ever online was 388, 07-01-2007 at 02:54 AM. |
|
All times are GMT -5. The time now is 08:01 AM.