Turning on lamp trips circuit breaker
When I turn on the lamp connected to one particular wall socket it trips the circuit breaker. My house is only one year old so I really don't think it's due to age. I thought it could be the lamp but I switched to a different lamp for that particular socket and though it worked well for a few weeks it is now back to tripping the circuit breaker. Any ideas on what it could be and how I can fix the problem? Thanks for any advice you can give.
Regards.
|

10-30-2006, 03:40 AM
|
|
|
Handyman
|
|
Join Date: Sep 2004
Location: Aliso Viejo, CA..
Posts: 129
|
|
|
Receptacles generally do not exist as "stand alone", so identify the several others controlled by this breaker and try your lamp/s there. If the tripping is not replicated, there are a couple of possibilities.
Check the wiring of the offending recep., the wiring may be bruised and shorting together or to ground.
Another is that there may be a staple nailed to tightly or having bruised the romex. The first staple away from the recep, box will be within 12" of that box.
__________________
Illegitimas non-carborundum
|

10-30-2006, 11:37 AM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,838
|
|
|
how many watts is the light bulb? do you have access to a clamp around ammeter? just thinking that the load on that circuit may be borderlined for the breaker.
|

10-30-2006, 01:25 PM
|
|
|
New Member
|
|
Join Date: Jan 2006
Location: .
Posts: 6
|
|
|
26W Flourescent
This seems to be the only outlet that is causing difficulties. All the others connected to the breaker are working perfectly. I unscrewed the outlet out of the wall and discovered that the black wire was about 1/8 inch out of the receptacle. I pushed it in fully and it seems to work fine now.....hopefully that was the reason behind the failure.
|

10-30-2006, 07:39 PM
|
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,838
|
|
|
OK it appears that - that was the problem. I have no idea other than speed why contractors are still using quick wire receptacles. They are a pain in the you know what especially when they are used to continue the neutral to other parts of circuits.
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 10,154
Threads: 6,798
Posts: 28,098
Top Poster: HayZee518 (3,838)
|
| Welcome to our newest member, The zzz Man |
» Links |
|
» Online Users: 44 |
| 0 members and 44 guests |
| No Members online |
| Most users ever online was 388, 07-01-2007 at 02:54 AM. |
|
All times are GMT -5. The time now is 08:50 AM.