Home Repair Forum



Reply
 
LinkBack Thread Tools Display Modes
  #11 (permalink)  
Old 11-13-2006, 09:13 PM
Speedy Petey's Avatar
Handyman
 
Join Date: Nov 2006
Location: Upstate, NY
Posts: 144
Speedy Petey is on a distinguished road
Actually I did not mix terms. Grounded, and grounding, are two very different things.

Also, you sometimes do connect a black wire to a white wire. Although newer codes require re-marking of the white wire to a "hot" color.
In an older installation it is very common to see a white connected to a black.
This is done in switch loops.
__________________
No, that's not me in the avatar. I just like the picture.
Reply With Quote
  #12 (permalink)  
Old 11-14-2006, 08:32 AM
Handyman
 
Join Date: Sep 2006
Posts: 37
leodlion is on a distinguished road
Quote:
Originally Posted by Speedy Petey View Post
Actually I did not mix terms. Grounded, and grounding, are two very different things.

Also, you sometimes do connect a black wire to a white wire. Although newer codes require re-marking of the white wire to a "hot" color.
In an older installation it is very common to see a white connected to a black.
This is done in switch loops.
The response I made was made to help the guy fix his electrical circuit problem. Your response is to find erroneously little bits of exceptions to the rule... get a life man.
Reply With Quote
  #13 (permalink)  
Old 11-14-2006, 02:54 PM
Speedy Petey's Avatar
Handyman
 
Join Date: Nov 2006
Location: Upstate, NY
Posts: 144
Speedy Petey is on a distinguished road
Quote:
Originally Posted by leodlion View Post
The response I made was made to help the guy fix his electrical circuit problem. Your response is to find erroneously little bits of exceptions to the rule... get a life man.
Pardon me? Who the hell are you?
How about you don't give advice you are NOT qualified to give. I was trying to correct the erroneous advice you gave so no one else would read it and make a mistake because of it.
If you look back you'll see I am not the only one questioning you either.

You stick to your trade, I'll stick to mine!
__________________
No, that's not me in the avatar. I just like the picture.
Reply With Quote
  #14 (permalink)  
Old 11-15-2006, 06:59 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,838
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
speedy & leo. this forum is not for you guys to straighten out your differences, take that up somewhere else.
The poster had a problem with his wiring. He made a boo-boo while replacing a light - let's stick to that! In answer to one of you guys statements, connecting a hot to a neutral will always trip a breaker and NOT always fry the circuit depending on the breaker rating and cycle time to trip. A white is used in switch loops for three ways and single pole switches. They should make 12 and 14/2 with two blacks for switch loops also a three wire just for switch and traveler lines. In some cases the white in a three way is used for carrying the neutral to the load or is hot depending on switch position.
Reply With Quote
  #15 (permalink)  
Old 11-15-2006, 07:12 AM
Speedy Petey's Avatar
Handyman
 
Join Date: Nov 2006
Location: Upstate, NY
Posts: 144
Speedy Petey is on a distinguished road
There are no differences. I simply tried to clear up some erroneous information and was insulted for doing so.


Your logic about making different cables for switch loops and 3-ways is the logic behind the newer code to re-mark the white in such applications.
__________________
No, that's not me in the avatar. I just like the picture.
Reply With Quote
  #16 (permalink)  
Old 11-15-2006, 07:52 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,838
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
New code? I have a copy of the 1996 code book right in front of me. Article 200-7, exceptions 1 & 2 deal with the white or natural gray wire. Go read exception #2.
Reply With Quote
  #17 (permalink)  
Old 11-15-2006, 10:23 PM
Speedy Petey's Avatar
Handyman
 
Join Date: Nov 2006
Location: Upstate, NY
Posts: 144
Speedy Petey is on a distinguished road
I don't have access to my '96 right now.

I said "newer", meaning less than 20 years old. The re-marking the white wire in a switch loop is a relatively new requirement. 200.7(C)(2)

It is very common to see homes built in the 50's-80's with black and white switch loops. Black and white on a switch and a black connected to a white at the fixture box.

That was my point about the inaccuracy of a "black never connected to a white".
__________________
No, that's not me in the avatar. I just like the picture.

Last edited by Speedy Petey; 11-15-2006 at 10:27 PM.
Reply With Quote
  #18 (permalink)  
Old 11-16-2006, 11:49 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,838
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
I apprenticed in Buffalo NY under a master elect. in 1965. We always taped a white in a switch loop - end of story.
Reply With Quote
  #19 (permalink)  
Old 11-17-2006, 06:50 AM
Speedy Petey's Avatar
Handyman
 
Join Date: Nov 2006
Location: Upstate, NY
Posts: 144
Speedy Petey is on a distinguished road
Agree, it was common practice for some. It just didn't become an official code till NEC '99.
Unfortunately tape is not legal to fulfill this code requirement.

For anyone interested, here is the code section and Handbook commentary in blue:

200.7(C)(2) Where a cable assembly contains an insulated conductor for single-pole, 3-way or 4-way switch loops and the conductor with white or gray insulation or a marking of three continuous white stripes is used for the supply to the switch but not as a return conductor from the switch to the switched outlet. In these applications, the conductor with white or gray insulation or with three continuous white stripes shall be permanently reidentified to indicate its use by painting or other effective means at its terminations and at each location where the conductor is visible and accessible.

Previous editions of the Code permitted switch loops using a white insulated conductor to supply the switch but not as the return conductor to supply the lighting outlet. Prior to the 1999 NEC, re-identification of this particular ungrounded conductor was not required. However, many electronic automation devices requiring a grounded conductor are now available for installation into switch outlets. Therefore, re-identification of all ungrounded conductors that are white or otherwise identified by one of the methods permitted for grounded conductors is now required at every termination point to avoid confusion and improper wiring at the time a switching device is installed or replaced. The required re-identification must be effective, permanent, and suitable for the environment, to clearly identify the insulated conductor as an ungrounded conductor.
__________________
No, that's not me in the avatar. I just like the picture.
Reply With Quote
Reply

Bookmarks



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Stats
Members: 10,154
Threads: 6,798
Posts: 28,098
Top Poster: HayZee518 (3,838)
Welcome to our newest member, The zzz Man
» Links

» Online Users: 38
0 members and 38 guests
No Members online
Most users ever online was 388, 07-01-2007 at 02:54 AM.
Powered by vBadvanced CMPS v3.0.1

All times are GMT -5. The time now is 08:20 AM.


A vBSkinworks Design
Powered by vBulletin® Version 3.7.2
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0