02-05-2007, 10:51 AM
|
 |
New Member
|
|
Join Date: Feb 2007
Location: Mannford, Oklahoma
Posts: 3
|
|
Two Breaker Panels
Greetings!
I am working on a double wide home we just recently had setup. Currently it has a 100amp G.E. (General Electric) Panel. There is no room to add anymore breakers. I want to switch the gas furnace (coleman presidential 2 77,000btu) to an electric furnace, gas hot water tank to electric and gas stove to electric. SO what I am really wanting is to make this Double wide total electric (outlets, lights, stove, water heater, ac, furnace, dryer, computers, and ect.)
I purchased another 100amp G.E. Main Box (20 1" spaces) with copper bus bar thinking I could just piggy back off the existing panel to give me a total of 200amps. The box at the pole will be 200amp. I would be using the new box pretty much just for the items I want to convert from gas to electric.
I did this rather than get a main lug sup panel because with using a 100amp sub panel tying to a 100am breaker in main box I still only get 100amps if I can pig tail off main than I can have a combined 200amps.
Do I have this all screwed up. I have already purchased the G.E. 100 amp main, so no matter what I need to make this work with my existing panel, I just need some guidance.
__________________
Thank You
Martin Maynard
In Memory of our Daughter
Bailey DeLonais Maynard
January 13, 2005-March 28, 2005
S.I.D.S. It's REAL!!!
www.healingokhearts.org
Last edited by mdmaynard : 02-05-2007 at 04:37 PM.
|

02-06-2007, 07:27 PM
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,379
|
|
|
the downlead for a 200 amp service is 4/0-3 seu aluminum. there is no way in heck a 4/0 wire is going to fit a 100 amp breaker. a way you can get around this is to install a trough at the bottom or top of the two service entrance panels with its own 100 amp breaker. the #2 feeders to the panels are then spliced to the 4/0 cables. because the main cable is aluminum an oxidant MUST be used and split bolt connectors al and cu rated and torqued to manufacturer specs. You then tape up the splices.
|

02-06-2007, 07:47 PM
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,379
|
|
|
Service entrance
Try this diagram see if this will work for you.
|

02-07-2007, 08:01 AM
|
 |
New Member
|
|
Join Date: Feb 2007
Location: Mannford, Oklahoma
Posts: 3
|
|
|
Thanks HayZee518!
I have read many posts and your replys and respect your opinion. After I posted I actually recieved the wire that will be running from the pole to the Double Wide and knew then that it was to big to do as I was thinking.
A huge huge huge thanks for the diagram, makes more sense to me now.
Just to double check, once I use a trough I can run 100am (in theory) to each panel? Is this correct?
Also just for clearification: On some other posts I see that when someone installs a 'sub-panel' the ground is isolated and not bonded. In my situation would I need to treat either panel as a sub or would they both be considered 'main'?
__________________
Thank You
Martin Maynard
In Memory of our Daughter
Bailey DeLonais Maynard
January 13, 2005-March 28, 2005
S.I.D.S. It's REAL!!!
www.healingokhearts.org
|

02-07-2007, 08:19 AM
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,379
|
|
|
IF the original panel was feeding the second panel it would be called a sub panel, BUT because it will be coming off the mains it is a service panel and neutral bonding will be necessary, not isolated as in a sub-panel. The disconnecting means for the main cannot be more than 6 motions of the hand -- meaning not more than 6 disconnects. You are using only two motions so you are within the code.
|

02-07-2007, 09:03 AM
|
 |
New Member
|
|
Join Date: Feb 2007
Location: Mannford, Oklahoma
Posts: 3
|
|
|
Agains thanks for your feedback.
I apologize for using the incorrect term ". . .ground is isolated and not bonded", this should have Neutural should replace ground. in that sentence.
I will let you know how it all works out in the end.
__________________
Thank You
Martin Maynard
In Memory of our Daughter
Bailey DeLonais Maynard
January 13, 2005-March 28, 2005
S.I.D.S. It's REAL!!!
www.healingokhearts.org
|

02-07-2007, 09:42 AM
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,379
|
|
|
you can contact me direct if you have yahoo im. handle there is buffalo12980
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
 |
» Forum Navigation |
|
|
» Links |
|
» Online Users: 21 |
| 0 members and 21 guests |
| No Members online |
| Most users ever online was 388, 07-01-2007 at 01:54 AM. |
|