Question Two Breaker Panels

Greetings!

I am working on a double wide home we just recently had setup. Currently it has a 100amp G.E. (General Electric) Panel. There is no room to add anymore breakers. I want to switch the gas furnace (coleman presidential 2 77,000btu) to an electric furnace, gas hot water tank to electric and gas stove to electric. SO what I am really wanting is to make this Double wide total electric (outlets, lights, stove, water heater, ac, furnace, dryer, computers, and ect.)

I purchased another 100amp G.E. Main Box (20 1" spaces) with copper bus bar thinking I could just piggy back off the existing panel to give me a total of 200amps. The box at the pole will be 200amp. I would be using the new box pretty much just for the items I want to convert from gas to electric.

I did this rather than get a main lug sup panel because with using a 100amp sub panel tying to a 100am breaker in main box I still only get 100amps if I can pig tail off main than I can have a combined 200amps.

Do I have this all screwed up. I have already purchased the G.E. 100 amp main, so no matter what I need to make this work with my existing panel, I just need some guidance.
__________________
Thank You
Martin Maynard
In Memory of our Daughter
Bailey DeLonais Maynard
January 13, 2005-March 28, 2005
S.I.D.S. It's REAL!!!
www.healingokhearts.org

Last edited by mdmaynard : 02-05-2007 at 04:37 PM.
Reply With Quote
  #2 (permalink)  
Old 02-06-2007, 07:27 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,342
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
the downlead for a 200 amp service is 4/0-3 seu aluminum. there is no way in heck a 4/0 wire is going to fit a 100 amp breaker. a way you can get around this is to install a trough at the bottom or top of the two service entrance panels with its own 100 amp breaker. the #2 feeders to the panels are then spliced to the 4/0 cables. because the main cable is aluminum an oxidant MUST be used and split bolt connectors al and cu rated and torqued to manufacturer specs. You then tape up the splices.
Reply With Quote
  #3 (permalink)  
Old 02-06-2007, 07:47 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,342
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
Service entrance

Try this diagram see if this will work for you.
Attached Images
File Type: jpg ENTRANCE.JPG (28.8 KB, 12 views)
Reply With Quote
  #4 (permalink)  
Old 02-07-2007, 08:01 AM
mdmaynard's Avatar
New Member
 
Join Date: Feb 2007
Location: Mannford, Oklahoma
Posts: 3
mdmaynard is on a distinguished road
Send a message via Yahoo to mdmaynard
Thanks HayZee518!

I have read many posts and your replys and respect your opinion. After I posted I actually recieved the wire that will be running from the pole to the Double Wide and knew then that it was to big to do as I was thinking.

A huge huge huge thanks for the diagram, makes more sense to me now.

Just to double check, once I use a trough I can run 100am (in theory) to each panel? Is this correct?

Also just for clearification: On some other posts I see that when someone installs a 'sub-panel' the ground is isolated and not bonded. In my situation would I need to treat either panel as a sub or would they both be considered 'main'?
__________________
Thank You
Martin Maynard
In Memory of our Daughter
Bailey DeLonais Maynard
January 13, 2005-March 28, 2005
S.I.D.S. It's REAL!!!
www.healingokhearts.org
Reply With Quote
  #5 (permalink)  
Old 02-07-2007, 08:19 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,342
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
IF the original panel was feeding the second panel it would be called a sub panel, BUT because it will be coming off the mains it is a service panel and neutral bonding will be necessary, not isolated as in a sub-panel. The disconnecting means for the main cannot be more than 6 motions of the hand -- meaning not more than 6 disconnects. You are using only two motions so you are within the code.
Reply With Quote
  #6 (permalink)  
Old 02-07-2007, 09:03 AM
mdmaynard's Avatar
New Member
 
Join Date: Feb 2007
Location: Mannford, Oklahoma
Posts: 3
mdmaynard is on a distinguished road
Send a message via Yahoo to mdmaynard
Agains thanks for your feedback.

I apologize for using the incorrect term ". . .ground is isolated and not bonded", this should have Neutural should replace ground. in that sentence.

I will let you know how it all works out in the end.
__________________
Thank You
Martin Maynard
In Memory of our Daughter
Bailey DeLonais Maynard
January 13, 2005-March 28, 2005
S.I.D.S. It's REAL!!!
www.healingokhearts.org
Reply With Quote
  #7 (permalink)  
Old 02-07-2007, 09:42 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,342
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
you can contact me direct if you have yahoo im. handle there is buffalo12980
Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Forum Navigation
     > Forum News
     > Illustrations
     > You Gotta Laugh!
     > Catch All
     > Plumbing
     > Electrical
     > Flooring
     > Wall Coverings
     > HVAC
     > Stenciling
     > Appliances
     > Audio & Video
     > Projects
     > Faux Painting
     > Painting
     > Gardening
     > Decks & Fences
     > Outdoor Projects
     > Garage Doors
» Links

» Search

Home Repair Forum
Google   
» Online Users: 24
1 members and 23 guests
Alaskaman
Most users ever online was 388, 07-01-2007 at 01:54 AM.
Powered by vBadvanced CMPS v2.2.0

All times are GMT -5. The time now is 02:21 PM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0