Electrical Wiring Overkill?

I am in the process of doing the wiring for my basement and I need some advice as to what wiring I should be using for the receptacles. The following was my original plan than I went to the home store and realized that this may get very expensive. I have read that 15A / 14G wire is ok for general purpose (excludes dedicated circuits) outlets - is this being penny wise and pound foolish?

20A Circuit / 12G - receptacles throughout the basement with a limit of 10 receptacles per 20A circuit.

20A Circuit / 12G dedicated for Electric Baseboard Heating

20A Circuit / 12G dedicated for 3 receptacles for Bar Area (includes GFCI)

20A Circuit / 12G dedicated for Sewage Ejector Pump

20A Circuit / 12G dedicated for Freezer (14CubicFt)

20A Circuit / 12G dedicated for Bathroom (includes GFCI)
Reply With Quote
  #2 (permalink)  
Old 06-27-2007, 12:02 PM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,548
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
you're on the right track. 12 ga/ 20 amp circuits are not overkill. many dwellings use 12 for lighting as well as power. besides the cost savings between 14 ga and 12 ga is minimal.
Reply With Quote
  #3 (permalink)  
Old 06-28-2007, 03:39 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,548
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
let me add something - a duplex receptacle is rated at 180 va per device. this amounts to an amp and a half per receptacle. change your number of outlets on a 20 amp circuit to 13 and you'll be in the ballpark.
Reply With Quote
  #4 (permalink)  
Old 07-25-2007, 08:24 AM
New Member
 
Join Date: Jul 2007
Posts: 22
normel is on a distinguished road
I know this thread is a little old, but I wanted to add a few things:

1. There is no limit to the number of receptacles you can have on a circuit in a dwelling (unless local codes say otherwise).
2. It is much easier to work with 14ga wire for lighting circuits, especially when you have multigang switch boxes.
3. As of 7/24/07, the difference in price between a 250ft roll of 12/2 and 14/2 is about $25.00. I wouldn't call that negligible. Use 14ga wherever you can.
Reply With Quote
  #5 (permalink)  
Old 07-25-2007, 08:40 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,548
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
normel - I beg to differ on the number of outlets on a circuit. code says loading per outlet is 180 va per outlet. this works out to an amp and a half per outlet. divide 20 by 1.5 and you'll get 13. 14 gauge wire on a 15 amp breaker allows you 10 receptacles. I wired houses for 35 years and used combination wiring 14 - 12 gauge. I used 14 for general wiring and a few rooms BUT dedicated circuits always 12 gauge.
Reply With Quote
  #6 (permalink)  
Old 07-25-2007, 08:59 AM
New Member
 
Join Date: Jul 2007
Posts: 22
normel is on a distinguished road
Article 220.13 (2002 NEC): "In other than dwelling units, receptacle loads computed at not more than 180 volt-amperes per outlet... "

Unless local codes stipulate otherwise, there is no limit for a dwelling per the NEC.
Reply With Quote
  #7 (permalink)  
Old 07-25-2007, 08:59 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,548
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
Quote:
Originally Posted by normel View Post
I know this thread is a little old, but I wanted to add a few things:

1. There is no limit to the number of receptacles you can have on a circuit in a dwelling (unless local codes say otherwise).

2. It is much easier to work with 14ga wire for lighting circuits, especially when you have multigang switch boxes.

3. As of 7/24/07, the difference in price between a 250ft roll of 12/2 and 14/2 is about $25.00. I wouldn't call that negligible. Use 14ga wherever you can.
Fine! If that be the case put 100 receptacles on one circuit and see what happens!
Granted 14 ga is a lot easier to work with, works great with lighting circuits but most contractors use 12 ga throughout new construction. This way they only have to inventory 12 ga
Reply With Quote
  #8 (permalink)  
Old 07-25-2007, 09:40 AM
New Member
 
Join Date: Jul 2007
Posts: 22
normel is on a distinguished road
Quote:
Originally Posted by HayZee518 View Post
Fine! If that be the case put 100 receptacles on one circuit and see what happens!
Absolutely nothing! It is not the number of receptacles, but what is plugged in to them.

BTW, I do not condone being excessive with the number of receptacles on a general use circuit and try to stay within 15-20 myself. My point is, according to the NEC, there is no limit for a dwelling and to say otherwise is incorrect.
Reply With Quote
  #9 (permalink)  
Old 07-26-2007, 11:33 PM
KSever's Avatar
Handyman
 
Join Date: Oct 2005
Location: Wisconsin ---> Moving to St. Louis
Posts: 74
KSever is on a distinguished road
Send a message via AIM to KSever Send a message via Yahoo to KSever
Quote:
Originally Posted by normel View Post
Absolutely nothing! It is not the number of receptacles, but what is plugged in to them.

BTW, I do not condone being excessive with the number of receptacles on a general use circuit and try to stay within 15-20 myself. My point is, according to the NEC, there is no limit for a dwelling and to say otherwise is incorrect.

I'm just glad you're not wiring my house, even at 15-20 outlets you are taking a chance of overloading something.
I just rewired my complete downstairs and stayed at 10 outlets per 20 amp breaker because I know most of the outlets will have something plugged in. Did all this after I had a window A/C burn an old outlet and they had half of this 4200 sq.ft Victorian house on one breaker with aluminum wire on some runs, Grant you this house hadn't been rewired since the 40's but it's now all 12ga. and on a 200 amp service panel.

I'll stick with what Hayzee says, what he says is what I have always been taught.
Reply With Quote
  #10 (permalink)  
Old 07-27-2007, 06:16 AM
HayZee518's Avatar
Deity
 
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,548
HayZee518 is on a distinguished road
Send a message via AIM to HayZee518 Send a message via Yahoo to HayZee518
in the code book they say to rate a circuit at not more than 80%. a 20 amp circuit therefore says not more than 16 [20 times .80 = 16] and for a 15 amp circuit 12 outlets [ 15 times .80 = 12] also 20 divided by an amp and a half [1.5] will = 13 outlets. AND 15 divided by 1.5 = 10. I read where it said "other than dwellings" - no limit, but from the safety standpoint I'd stick with the calculation. Thanks KSever for your input!
Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

» Forum Navigation
     > Forum News
     > Illustrations
     > You Gotta Laugh!
     > Catch All
     > Plumbing
     > Electrical
     > Flooring
     > Wall Coverings
     > HVAC
     > Stenciling
     > Appliances
     > Audio & Video
     > Projects
     > Faux Painting
     > Painting
     > Gardening
     > Decks & Fences
     > Outdoor Projects
     > Garage Doors
» Links

» Search

Home Repair Forum
Google   
» Online Users: 23
0 members and 23 guests
No Members online
Most users ever online was 388, 07-01-2007 at 01:54 AM.
Powered by vBadvanced CMPS v2.2.0

All times are GMT -5. The time now is 02:03 AM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.1.0