07-10-2007, 07:22 PM
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,594
|
|
|
OK, both boxes in the garage will be classed as sub panel boxes. What you'll need for a feed for the 100 amp will be three THW/THWN #2 Aluminum cable in 1 1/2 inch conduit - pvc, rigid. You'll need to drive two ground rods at the external garage location. A #6 bare copper will be the ground wire size for the 100 amp. The panelbox adjacent to the 100 amp - the 60 amp is also classed as a sub panel. It also needs a #6 bare ground to the panel. A 60 amp feeder can be #6/3 with ground romex or three #6's THHN/THWN copper cables in a 1 inch conduit, again metal or pvc. Both sub panels need an isolated neutral strip and the addition of an auxillary ground strip to which the driven ground wire will attach.
|