Hello, I am wondering if there is such a beast as a box with multiple 240 volt receptacles. I have 6 different 240 volt power tools and would love to plug them all in to some sort of reciever on or under my workbench instead of running extension cords all over the place. I would love it if there was something I could wire into a 30 or 40 amp breaker and have 6 or more outlets in it. Thanks for the help.
|

10-19-2007, 06:03 AM
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,892
|
|
|
please list the amperages of each power tool. also what type of plug is on each tool? are they straight blade type or twist lock? would these tools all be running at the same time?
|

10-19-2007, 07:01 AM
|
|
New Member
|
|
Join Date: Oct 2007
Posts: 5
|
|
|
I am okay on the tools and amp ratings, I just really would like to know...
if there is a "receptacle box" type thing that can multiple 240 plugs... kind of like a surge protector, but for 240. I know better than to exceed the amps. Thank you.
|

10-19-2007, 07:05 AM
|
|
 |
Handyman
|
|
Join Date: Nov 2006
Location: Upstate, NY
Posts: 148
|
|
Quote:
Originally Posted by bestbowl
........but for 240.
|
That's not what Hazee asked. "240" is only half the equation. This is an extremely common DIY mistake.
What are the amperage draws (@240v) of each tool you will be using? What size receptacles do they require? This makes a BIG difference.
__________________
No, that's not me in the avatar. I just like the picture.
|

10-19-2007, 08:06 AM
|
|
New Member
|
|
Join Date: Oct 2007
Posts: 5
|
|
|
Thanks again and sorry to be so stubborn on this, but I morre than assure you I am
very solid on the amps. I would truly just like to know if there is some sort of power strip and/or surge protector that has multiple 240 recepticles that I can hard wire to a 30 or 40 amp 240 two pole circut breaker. I am sorry to be so repetitive but I would just like this question answered. I am 100% on the amperage. I am going to be running between 20 and 30 amps. Thanks again.
|

10-19-2007, 08:15 AM
|
|
New Member
|
|
Join Date: Oct 2007
Posts: 5
|
|
|
Oh and sorry, I did edit the orig. question, but it didn't make the correction...
The sockets are NEMA 6-20R
|

10-19-2007, 08:48 AM
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,892
|
|
|
ok NEMA 6 20 amp receptacles. NOW are they twist lock or other?
|

10-19-2007, 03:44 PM
|
|
New Member
|
|
Join Date: Oct 2007
Posts: 5
|
|
|
Not twist lock, just plug-in
Thanks again
|

10-19-2007, 03:56 PM
|
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,892
|
|
|
ok, now to answer your question. there's nothing stock made that you could use. you'll have to make up a 240 volt receptacle center. for that matter you can put outlets where you want in your garage - as far as using one breaker to feed them all, not such a good idea. Since a 240 volt motor doesn't use a neutral, 12/2 with ground would suit your project perfectly. feed all your outlets with a two pole 20 common trip breaker. The white wire in the cable, mark with black tape the white wire on both ends - if someone else goes into the panelbox, he should know that a tape wrapped white is 240 volts and not be used as a neutral. The bare ground goes to the green screw on the receptacle's yoke. For a DIY I'd recommend plastic nail on boxes.
|

10-19-2007, 06:28 PM
|
|
 |
Handyman
|
|
Join Date: Nov 2006
Location: Upstate, NY
Posts: 148
|
|
Quote:
Originally Posted by bestbowl
The sockets are NEMA 6-20R
|
THERE we go.
There is nothing you could use that you could plug into a 30 or 40 amp circuit. You CANNOT have 20A rated receptacles on a 30 or 40 amp circuit, unless of course there is some sort of overcurrent protection (circuit breakers or fuses) built in.
__________________
No, that's not me in the avatar. I just like the picture.
|
 |
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Stats |
Members: 10,238
Threads: 6,832
Posts: 28,283
Top Poster: HayZee518 (3,892)
|
| Welcome to our newest member, cbfiv |
» Links |
|
» Online Users: 45 |
| 1 members and 44 guests |
| No Members online |
| Most users ever online was 388, 07-01-2007 at 02:54 AM. |
|