Subpanel Ground Bar
Good Day. I purchased a Square D SubPanel for my basement and in the process of installing. I have a 100A Breaker from a Homeline Panel to the Subpanel. I connected the Ground to appropraite Bar as well as the Neutral to its place along with the hots to their place. The panel came with one ground bar which I installed on the left hand side of the panel - this is where I terminated the Ground Wire from the Main Panel. I purchased an additional Ground Bar and have installed it into the right side of the panel. I have concerns about using the additional ground bar as it is not grounded from the main panel like the one that is on the left hand side. Do the Ground Bars need to be connected via wire???
Thanks |
|
|
|
||||
|
SubPanel Setup
My apologies for the confusion from my last post - it was late. Nonetheless, I do appreciate the assistance.
This is what I have. I used #2 NM Cable from the main box to the subpanel with 3 conductors (Black, Red and White) and 1 bare ground wire. I connected the Black and Red to the respective Hot Lugs and the White to the Neutral Lug and finally the Bare Ground to the Ground Bar Hub that was included on the left hand side of the panel. My question is, can an additional Ground Bar to the right hand side of the panel to make the routing of the ground wires easier. If a Ground Bar can be added do I need to run a a bare copper line to the Ground Bar on the left han side of the panel? Thanks ever so much for the assistance. |
|
||||
|
Subpanel - Updated Drawing
Ok - I took the liberty to draw the subpanel as I have it currently. So, if I read what you said correctly it is ok to include an additional ground bar and that there is no need to connect the two ground bars together as the panel is bonded.
Let me know if I have this correct - pretty sure I do. Thanks |
![]() |
| Bookmarks |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | |
| Display Modes | |
|
|