Generator issue...
Used a Coleman 5000 Powermate generator today during the power outage. Found many things weren't working right. Started shutting stuff off right away. Light bulbs were popping, transformers were buzzing. Checked the output to find 186 V on each leg!!! It fried many electronic items, several cordless phone transfomers and three Belkin surge protectors.
The generator info is: Coleman Powermate. Powerbase 5000.
Model PM0545305.01. ACV 120/240. Current 41.6/20.8. Surge 6250.
Serial 78270386. Power factor 1.
What can I do to repair something like this? Is there a board that can be replaced? Or a relay? Also, any ideas on what could make it go haywire?
I will NEVER charge up my house again wthout first verifying the output on both legs!!
By the way...this is really strange...one leg on the breaker in the main was zero volts while the other was reading over 360!! At the generator receptical, however, it was 180(+) on each leg. THe engine rpm's were right on at 3600.
|

12-13-2007, 06:01 AM
|
 |
Handyman
|
|
Join Date: Nov 2006
Location: Upstate, NY
Posts: 134
|
|
|
It's obviously a problem inside the genny. Could be a board or electronic, but I doubt it at those voltages.
For a cheap genny like that I doubt it's worth fixing.
How are you hooked up to the house?
__________________
No, that's not me in the avatar. I just like the picture.
|

12-13-2007, 02:50 PM
|
 |
Deity
|
|
Join Date: Jul 2004
Location: Saint Regis Falls, NY, USA.
Posts: 3,534
|
|
|
the guts of a generator is the stator winding, a wirewound rotor, two diodes [and a set of slip rings and brushes] if there is a regulator. a utility generator relies on residual magnetism in the iron punchings of the rotor. current and voltage rely on how the stator is wired. voltage and frequency are the results of prime mover speed. most units keep the voltage from about 120 volts to possibly 135 volts. if something should happen to the stator, a winding shorts out, the resultant voltage could spike up. if the coleman doesn't used a wound rotor then there is only a permanent magnet as the rotor.
|

12-13-2007, 11:24 PM
|
|
King
|
|
Join Date: Jan 2004
Location: .
Posts: 866
|
|
|
Bad Genny.....
Speedy...am running the house by plugging into a 240 outlet.
HayZee...Since I like learnig stuff anyway, I'll take it apart and see if anything's obvious. If nothing, then I'll get a price from the local electric shop...
|

12-14-2007, 12:56 PM
|
|
New Member
|
|
Join Date: Jul 2007
Posts: 22
|
|
Quote:
Originally Posted by mrcaptainbob
Speedy...am running the house by plugging into a 240 outlet.
|
Through a transfer switch I hope??
|

12-14-2007, 09:55 PM
|
 |
Handyman
|
|
Join Date: Nov 2006
Location: Upstate, NY
Posts: 134
|
|
Quote:
Originally Posted by normel
Through a transfer switch I hope??
|
Doesn't sound like it. 
__________________
No, that's not me in the avatar. I just like the picture.
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
|
| Thread Tools |
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
 |
» Forum Navigation |
|
|
» Links |
|
» Online Users: 39 |
| 0 members and 39 guests |
| No Members online |
| Most users ever online was 388, 07-01-2007 at 01:54 AM. |
|
All times are GMT -5. The time now is 04:07 PM.